    Do floor outlets require covers?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Floor outlets

    Quote Originally Posted by mathew stouffer View Post
    Do floor outlets require covers?
    Matthew,

    Yes. They need to be specifically designed for floors. The outlet should be recessed below the surface of the floor and the plate should be strong enough to bear weight. I believe the box needs to be strong enough to bear weight as well.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  3. #3
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Floor outlets

    Thanks Gunnar.


  4. #4
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: Floor outlets

    Here is a copy & paste from the 2008 NEC which is unchanged from the 2002 & 2005 editions.
    314.27

    (C) Floor Boxes. Boxes listed specifically for this application
    shall be used for receptacles located in the floor.

    Exception: Where the authority having jurisdiction judges
    them free from likely exposure to physical damage, moisture,
    and dirt, boxes located in elevated floors of show
    windows and similar locations shall be permitted to be
    other than those listed for floor applications. Receptacles
    and covers shall be listed as an assembly for this type of
    location.

    This is my opinion, but that receptacle in the picture does not meet that exception.


  5. #5
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Floor outlets

    Thanks. Once I looked at the distrution panel I figured these had to be wrong It was a mess.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Floor outlets

    Quote Originally Posted by Rollie Meyers View Post
    Here is a copy & paste from the 2008 NEC which is unchanged from the 2002 & 2005 editions.
    314.27

    (C) Floor Boxes. Boxes listed specifically for this application
    shall be used for receptacles located in the floor.

    Exception: Where the authority having jurisdiction judges
    them free from likely exposure to physical damage, moisture,
    and dirt, boxes located in elevated floors of show
    windows and similar locations shall be permitted to be
    other than those listed for floor applications. Receptacles
    and covers shall be listed as an assembly for this type of
    location.

    This is my opinion, but that receptacle in the picture does not meet that exception.
    Rollie,

    "This is my opinion, but that receptacle in the picture does not meet that exception."

    Not just "your opinion, that is what the code states,

    That certainly does not look like it is "located in elevated floors of show
    windows and similar locations". "Similar locations" would be floor areas which are not used for walking on, but for display - which is what show windows are not for (not for walking on) and are for (displaying items).

    Additionally, when that exception is applied, the code states (bold and underlining are mine) "Receptacles and covers shall be listed as an assembly for this type of location".

    Thus it is safe to say that is not allowed as shown in the photo.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Floor outlets

    Let your mind picture a stout 200 + pound lady wearing stiletto heels coming down on that plastic receptacle outlet. I know........ Neither a pretty sight nor result.

    Jerry McCarthy
    Building Code/ Construction Consultant

  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Floor outlets

    Also, is it my imagination or an optical illusion ... that looks like it is in the middle of the top landing of a stairway, right where WC Jerry's referenced person will step on it.

    Even a 110 lady in spike heels will poke that thing out, heck, even a man in large flat heels like are on men's shoes will crush that thing.

    Not only that, but if on the landing as it looks, it is now a trip, slip and fall hazard as the surface is no longer level.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    danyackoyd's Avatar
    danyackoyd Guest

    Default Re: Floor outlets

    I don't know about you guys but this picture just doesn't seems to be save. I know that it always happens that the electric components you want to use, are the furthest away for the closes socket, but putting a raised socket into the floor boarding doesn't seem to be the alternative for me. I don't know if by covering the socket any issue would be resolved.