    Default Vent near gable

    Hi Folks,

    Just inspected a new home. Not allowed on the roof, so I couldn't take measurements. I did see a vent pipe about 1 1/2 feet under the gable vent. Per the P3103.5 (2006 IRC) you shouldn't have vents close to "air intakes" to the house. I just want a sanity check here (on the question only) Is the gable vent to the attic considered an air intake to the home, (I believe it is) but it's not like a window or door that goes into the living area. What's the call here? violation or not?
    (No I don't do code inspections, but do like to keep the new builders in line)

    Thanks!
    Waiting to finish report, thanks for your speedy replies.
    -Dave

    Similar Threads:
    Member Benefits1
    Dave Hill
    Buyers & Sellers Property Inspections LLC
    WWW.BuyersSellersPi.Com

  2. #2
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Vent near gable

    Was it a "sewer vent" or what?

    What was the vent to?

    Got any pics?

    rick


  3. #3
    Join Date
    Mar 2007
    Location
    Chandler, AZ
    Posts
    121

    Default Re: Vent near gable

    yes, it was a sewer vent. The one directly under the gable vent.
    Thanks for your help!

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Dave Hill
    Buyers & Sellers Property Inspections LLC
    WWW.BuyersSellersPi.Com

  4. #4
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: Vent near gable

    Yes, Bad planning and should not have been allowed. Did you send the broker into the attic to sniff around?


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Vent near gable

    As the others have said - no, not allowed, must be 10 feet from or 2 feet higher than those soffit vents.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Chandler, AZ
    Posts
    121

    Default Re: Vent near gable

    As always, thanks for the help!
    Have a groovy weekend!

    BTW, I already submitted the report saying it was not allowed, thanks for backing me up. 4th year as an inspector and it still helps to bounce ideas off of other professionals. The code books are great, but a little help in interpretation is priceless.

    Dave Hill
    Buyers & Sellers Property Inspections LLC
    WWW.BuyersSellersPi.Com

  7. #7
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: Vent near gable

    I reported the same a year or so ago. Mold in that area of the attic. I took a beating on that one. Neither the "plumber" nor the "mold remediator" agreed with me. Oh well! No referrals as a result of that job.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Eric Barker, ACI
    Lake Barrington, IL

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •