    Default weatherproof breakers allowed ??

    This is the first time i have seen breakers oustide the box, used for the A/C has no water proof cover are they rated to do this? any thoughts. I recommended to add a cover or replace the box

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: weatherproof breakers allowed ??

    Quote Originally Posted by mike huntzinger View Post
    replace the box

    That's the only option.

    The entire enclosure needs to be rated for outdoor use. That will come with a different enclosure, dead front cover, and a weatherproof cover.