    Default PRESSURE VALVE DONE BY JOE THE PLUMBER

    HEY ALL
    i did this 1999 house today. all was well untill i started testing the bathrooms. in the second floor bath, cold water pressure was satisfactory and i filled the sinks and tub to check drainage and all was well. then i turned on the hot water in both sinks and followed with the tub hot water. the water in the sinks literally became a drip. i'm guessing i can pee with more pressure. all other bathrooms the same-there were four. so curiosity got me .off i went to check if water heater was turned on and if it was,then i checked pressure at tank. pressurs at tank was a mind blasting 120 + psi.
    next i went to main house water shut off valve and holy *&#$ this is what i found.---owner was a Ball Aerospace rocket scienctis--and original owner
    do you think builder did this or joe the plumber sprinkler guy after building inspection

    what do u think
    charlie

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: PRESSURE VALVE DONE BY JOE THE PLUMBER

    Your a brave man opening up that drain valve on the water heater. Most will never shut back off and will continously drip.

    rick


  3. #3
    Richard Pultar's Avatar
    Richard Pultar Guest

    Default Re: PRESSURE VALVE DONE BY JOE THE PLUMBER

    what did you find ?


  4. #4
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: PRESSURE VALVE DONE BY JOE THE PLUMBER

    Charlie,

    The setup looks like a house with fire sprinklers to me. The valve at the lower/left looks like it shuts off everything, the valve in the center is the main shutoff for the domestic water supply, the valve at the lower/right might be a drain-down, but is more likely a fire sprinkler alarm test.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  5. #5
    Richard Pultar's Avatar
    Richard Pultar Guest

    Default Re: PRESSURE VALVE DONE BY JOE THE PLUMBER

    it looks like a water supply valve to a boiler to me .with a easy system drain down .for a winter close. where no heat is left on .
    I don't get the bonding jumper, it's like a meter is missing... maybe a well ? I doubt this arrangement has anything to do with the flow restrictions.. my first guess is sediment on the airators or just half inch pipe trying to do too much


  6. #6
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: PRESSURE VALVE DONE BY JOE THE PLUMBER

    GUNNAR

    that valve is for the sprinkler sysytem--there is not fire system in house

    RICHARD

    no boiler --theres a furnace

    any other thoughts----120psi at water heater tells me i have no pressure relief valve from street on main side

    thanks all
    charlie


  7. #7
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: PRESSURE VALVE DONE BY JOE THE PLUMBER

    Charlie,

    Yes, the high pressure is clearly a problem. When you have a pressure reducing valve, it is necessary to have an expansion tank on the water heater. The part that puzzles me is why the low flow with the really high pressure. That part is weird. Once again, use the home inspectors' mantra. Ommm... defer.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  8. #8
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: PRESSURE VALVE DONE BY JOE THE PLUMBER

    Anything made by man can and eventually will fail.

    That pressure reducing valve may not be cranked down or it could have failed. See the screw down stem? So can little kids. Also, they can clog. Happens to boiler feeds all the time, which is why many now have strainers and a bypass for when the strainer clogs.

    As for the low/ no flow problem, there could be a hidden valve that is 90% closed.

    Regardless, you did your part by identifying at least three problems with the plumbing: ultra-high pressure, flow restriction and an uncapped line off that ball valve just waiting to flood the basement.

    Just understand you can have very high pressure with almost no flow. I had a similar problem with a gas fireplace. The pilot would light but when you fired the burner, it dropped out. I had 6.54 wci inlet pressure static but it dropped to less than 1 inch when firing. Disconnected flex connector and took readings right off shutoff. Same. Shut off meter. Removed gas cock and found the plastic protective plug still in there. The OJT rookie plumber doped the threads and screwed the gas cock on without removing the dust plug. The tiny hole torn in the plastic allowed it to function like a shower head flow restrictor> pressure with low flow.

    Where is the backflow preventer?

    Keep the fire in the fireplace.

  9. #9
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: PRESSURE VALVE DONE BY JOE THE PLUMBER

    Not sure I would test pressure at a water heater drain. But to each his own.
    Did you happen to take off any of the strainers?
    Did you take a pressure reading at any other fixture?

    1999, so it is not likely a bad dip tube clogging the faucet aerators.