Results 1 to 5 of 5
  1. #1
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default HOME OWNER WOOD STOVE INSTALL

    HEY ALL

    found this wood stove yesterday, and things don't look safe.

    is there proper clearance to combustable material in that garage vent to chimney,and is that safe to have the vent pipe exposed like that in garage ??
    last question,what is the code # for such,is it 1306.1 IRC

    thanks
    charlie

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Michael Larson's Avatar
    Michael Larson Guest

    Default Re: HOME OWNER WOOD STOVE INSTALL

    Charlie,

    That looks like type HT vent. It requires 2" clearance to combustibles.

    On second look I see a paper label that I can't make out. What does it say?

    It could be triple wall which usually requires 1" to combustibles.

    HT should have a marking on the pipe but is is hard to make out sometimes as it is embossed in the metal.

    It's best to consult the stove mfgs. instructions for clearances of the stove and vent.


  3. #3
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: HOME OWNER WOOD STOVE INSTALL

    Charlie,

    I rarely see these things installed correctly - everything goes back to manufacturer specs which few people pay any attention to. In the garage there should be a chase around the vent so that combustibles cannot be set up against it. The brick behind the stove, if that's what it is, will generally have a 1 inch air space requirement between it and the wall behind it.

    Eric Barker, ACI
    Lake Barrington, IL

  4. #4
    Join Date
    Jun 2008
    Location
    Delmar NY
    Posts
    157

    Default Re: HOME OWNER WOOD STOVE INSTALL

    That vent pipe looks like it has dents in it, or is that just a reflection. It does need protection from combustibles and from being damaged or punctured.


  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool job security

    The references for the stove installation itself revert back to the stove listed instructions. If the stove is not listed, then refer to NFPA 211.
    If the brick wall is not ventilated with a 1" air space per NFPA 211, then it reduces the clearance to the combustible wall by 33%, whereas a the same brick with a 1" ventilated space yields a 66% reduction.

    The factory chimney is solid packed listed to 103HT rated at 2,100F with a 2" clearance to combustibles. This chimney must be protected from damage or incidental contact by people. Also, the listed firestop/ radiation shield is missing.

    Flag it for a Level II inspection and you're done.

    Good catch Charile and thx for using lower case letters!

    Keep the fire in the fireplace.