Thread: VTR flashings

  1. #1
    Jerome W. Young's Avatar
    Jerome W. Young Guest

    Default VTR flashings

    should the leading edge of this lead flashing not be under the preceding tile? It was caulked to the surface of the tile as is all the other vents. Is this a dry system when they do it this way. The under layment looked like felt paper.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: VTR flashings

    1) Yes
    2) No


  3. #3
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: VTR flashings

    If not leaking now and I am guessing it already is, it is a leak waiting to happen. If all the vents are like that it is going to get a little costly to do them all right.


  4. #4
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: VTR flashings

    Yes, and Jerome you have a nice camera and I'm ah-hm, borrowing your photos.
    Thanks

    Wayne, why the "no" vote?

    Jerry McCarthy
    Building Code/ Construction Consultant

  5. #5
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: VTR flashings

    Is this a dry system when they do it this way.

    In answer to that part, No it is not a dry system.
    But wait a minute.

    As most brokers would say.
    "well, it's not leaking now is it?"
    So it's dry? Now?

    TOOOOEY!!!!!


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: VTR flashings

    That would be an improperly done System 1 tile roof.

    Not only is the flashing installed incorrectly, but the base of the flashing is too small to serve that purpose. That is a regular VTR lead flashing, System 1 flashings need to be wider and longer, both up under the tile above and down over the tile it is through.

    This looks like a System 1 flashing, yet in the second photo, that exhaust roof cap is not flashed like that. Something is screwy (but this is obvious).

    The underlayment likely *is* 43# felt, that is what was typically used for System 1 tile roofs.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired