    imported_John Smith's Avatar
    imported_John Smith Guest
    Default AC Condensor Location - This is a new one for me
    Older house with pool. AC condensing unit located about 60' from home with line set and electrical buried under ground. Thoughts?
    Default Re: AC Condensor Location - This is a new one for me
    I had the same question sometime ago.
    http://www.inspectionnews.net/home_i...-distance.html
    If I am not mistaken it is around 25 feet max before efficiency starts dropping of drastically/ Could be wrong
    I think that might be true with a heatpump in the heating mode, but don't see any reason for A/C or heatpump in the cooling mode.
    Im not sure why someone would do this other than they dont like the look of a condensor or the noise. I saw plenty of places around the house where they could have put it with minimal visual exposure/noise. I believe the electrical is only ran in the flex (if even that once its underground, hard to say).
    At first, I thought I must be imagining things. I walked around the house several times before I finally found it (buried in a bunch of shrubbery). Also not an electrical disconnect in close proximity.
    Was the disconnect within sight of the unit?
    Ron Bibler's Avatar
    Ron Bibler Guest
    Where is the shut off ?
    Best
    Ron
    No separate shut off, however the main panel was somewhat within the line of sight (if you removed the vegetation around the condensing unit).
    Sounds like a judgement call, (IRC 4001.5 Disconnect in sight of equipment). I don't think I would write it up.
    Default Re: AC Condenser Location - This is a new one for me
    From the other thread:
    Check the manufactures' "long line" requirements, both horizontal and vertical separation have to be considered.
    For example, here's Carrier's requirements for residential Puron units:
    http://www.xpedio.carrier.com/idc/gr...t/llgp-2xa.pdf
    Note line lengths of up to 200 feet (100 feet away), and up to 250 feet equivalent line lengths.
