    Default Re: Breaker position

    From the archives:

    From the 2002 NEC:
    240.81 Indicating.
    - Circuit breakers shall clearly indicate whether they are in the open “off” or closed “on” position.
    - Where circuit breaker handles are operated vertically rather than rotationally or horizontally, the “up” position of the handle shall be the “on” position.