    Can some one determine the amps on this one. it has 2, 600 volt wires and one to the neutral bus bar. i hope i insert the pictures right.

    Similar Threads:
    Attached Files Attached Files
    Last edited by Jason Schmidt; 01-15-2009 at 12:03 AM. Reason: no picture
    Inspection Referral

  2. #2
    Ron Bibler's Avatar
    Ron Bibler Guest

    Default Re: stab lock

    No photos in the post..

    Best

    Ron


  3. #3
    Jason Schmidt's Avatar
    Jason Schmidt Guest

    Default Re: stab loc

    Got the picture in this time.


  4. #4
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: stab lock

    Since it's a FPE panel, it's tempting to answer ZERO AMPS, because how can it have any current flowing when it's sitting in the trash out on the sidewalk?

    However, see where it says AL 2 AWG on one of the hot legs? That would be 100 amp service.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  5. #5
    Join Date
    Mar 2007
    Location
    Georgetown, KY
    Posts
    538

    Default Re: stab lock

    Erby Crofutt, Georgetown, KY - Read my Blog here: Erby the Central Kentucky Home Inspector B4 U Close Home Inspections www.b4uclose.com www.kentuckyradon.com
    Find on Facebook at: https://www.facebook.com/B4UCloseInspections

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: stab lock

    Quote Originally Posted by John Arnold View Post
    Since it's a FPE panel, ... in the trash out on the sidewalk?
    Quote Originally Posted by Erby Crofutt View Post
    It needs to be replaced anyway.
    Let's presume, in its current (pun intended) and existing condition, as shown in the photo that this is the "service equipment" - which it is with the meter below feeding it.

    There are 12 + 1 (having one empty space for another breaker) *Main Disconnects* in there. Only up-to-a-maximum-of 6 are allowed.

    Also note the overheated white wires, those coming off the breakers ...

    There there are the more-than-one neutrals in the neutral terminals.

    Then there is that large hole in the back with some contraption around the wires going through an extra-super-large knock out with brick and mortar showing.

    And then ...

    Let's see, Erby said it needed to be replaced and John said when you do to put it in the trash out on the sidewalk ...

    Yep, those are the best recommendations.

    The only recommendation which could improve on that would be to have the installing electrician do so at his own cost - no cost to anyone else - except he is likely long since retired, maybe not even on this Big Blue Planet Earth with us anymore either.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Jason Schmidt's Avatar
    Jason Schmidt Guest

    Default Re: stab lock

    Thank you so very much. I hope you all have a great day.