Results 1 to 13 of 13
    Jerome W. Young's Avatar
    Jerome W. Young Guest
    Default service entry cable sizing
    House had a 225 amp SqD breaker with
    [aluminum] 4/0 awg 600v rhh or rhw service
    The breaker itself indicated the following: #4-300mcm cu/al.
    I believe 4/0 can carry 200 amp max?
    Default Re: service entry cable sizing
    Correct. #4/0 AWG aluminum is rated for 200 amps.
    The rating on the breaker is for the approved conductor sizes allowed in the terminals.
    I'm sure you got the multiple tapped neutrals. For all those empty terminals, why on earth did they put 2 and 3 in the same terminal? Then the grounds too.
    Last edited by Jerry Peck; 01-16-2009 at 07:29 AM. Reason: correcting a typo Jeff pointed out - correcting #4 AWG to #4/0 AWG
    aren't they allowed 2 per terminal? three i know is wrong.
    Kevin Barre's Avatar
    Kevin Barre Guest
    Only one per terminal for neutrals. Typically two per terminal for the grounds -- IF they are the same gauge and material and meet size requirements. Read the paper instructions in the panel to let you know what this mfr allows.
    Quote Originally Posted by Kevin Barre View Post
    Plus, neutrals and grounds not allowed in same terminal. In same terminal bar, yes (if service equipment) ... in same terminal, no.
    Mount Pleasant, SC
    Correct. #4 AWG aluminum is rated for 200 amps.
    Apparently Jerry, you've never seen a lazy sub contractor's effort ... :-)
    www.atozinspector.com
    Jeff Remas's Avatar
    Jeff Remas Guest
    Do you mean 4/0 aluminum?
    Jeff Remas's Avatar
    Jeff Remas Guest
    Rhw can only handle 190A
    Rhh can only handle 205A
    If it is rated for both then the higher of the two applies.
    Quote Originally Posted by Jeff Remas View Post
    Yes, thanks, I went back and corrected it.
    Jeff,
    See: (underlining is mine)
    - Table 310.15(B)(6) Conductor Types and Sizes for 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. Conductor Types RHH, RHW, RHW-2, THHN, THHW, THW, THW-2, THWN, THWN-2, XHHW, XHHW-2, SE, USE, USE-2
    - - 4/0 aluminum - 200 amp (reading through the table from right under Aluminum to the left under Rating)
    Jeff Remas's Avatar
    Jeff Remas Guest
    Yes, I understand that but the cable is already rated at 205 so the 200A allowable ampacity for 4/0 aluminum in single family residences is not relevant since they used a higher rated conductor.
    That is still relevant as those are the allowable ratings for those conductors in dwelling unit service and feeder use.
    Wayne Price's Avatar
    Wayne Price Guest
    According to the California code, based on the NEC, 4/0 copper can handle 250 amps, while 4/0 aluminum or copper-clad aluminum will conduct 200 amps safely.
