Results 1 to 10 of 10
  1. #1
    SAL IACONO's Avatar
    SAL IACONO Guest

    Wink arc fault and bus bar

    Wanted to know if its Ok to tie the nuetral and ground together in the same hole on the bus bar (box is a C-H)? Also new TREC guidelines state arc fault protection required in the following areas :
    (17) the lack of arc-fault circuit
    interrupting devices serving family rooms,
    dining rooms, living rooms, parlors, libraries,
    dens, bedrooms, sunrooms, recreations rooms,
    closets, hallways, or similar rooms or areas;

    Does this include lights? i noted a few breakers labeled lights and was wondering if those needed to be listed as deficient as well.

    What is the best method to test these breakers?



    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: arc fault and bus bar

    Yes, it includes lights.
    You might as well develop a blanket statement covering AFCI deficiencies since I doubt you will see a fully compliant installation until the municipalities in your area adopt and fully enforce the 2008 NEC.
    Kind of like GFCI's for us years ago.
    Basically every light and outlet in the house that is not required to be GFCI protected needs AFCI protection.

    No, the neutral must be by itself in the terminal.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: arc fault and bus bar

    Quote Originally Posted by SAL IACONO View Post
    Wanted to know if its Ok to tie the nuetral and ground together in the same hole on the bus bar..
    No. 2006 IRC E3606.4.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: arc fault and bus bar

    The neutrals need to terminate one per hole. They cannot share with another neutral or grounding conductor.

    The only recognized way to test the AFCI function is with the test button on the breaker.

    The NEC says that the protection is for the outlets. The definition of outlet is " A point on the wiring system at which current is taken to supply utilization equipment". This includes lights and receptacles. Smoke alarms also need this unless local rules have overridden this.


  5. #5
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: arc fault and bus bar

    Quote Originally Posted by Jim Luttrall View Post
    ...
    Basically every light and outlet in the house that is not required to be GFCI protected needs AFCI protection...
    Could you explain this? Since GFCI and AFCI are two different beasts, why do circuits with GFCI protection not need AFCI protection?

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  6. #6
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: arc fault and bus bar

    I can't explain it, just what the code says.
    I am guessing the AFCI manufacturers gave this to the code writers since there would be a problem getting both types of protection on the same circuit.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  7. #7
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: arc fault and bus bar

    Quote Originally Posted by Jim Luttrall View Post
    I can't explain it, just what the code says.
    I am guessing the AFCI manufacturers gave this to the code writers since there would be a problem getting both types of protection on the same circuit.
    I'm just trying to understand this from a technical standpoint. Why is it a problem getting both types of protection on the same circuit? If you have an AFCI breaker protecting a circuit with GFCI receptacle outlets, do they interfere with each other in some way?

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: arc fault and bus bar

    Maybe in 2011...
    Again. I can't explain it, maybe someone else has a better idea.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    SAL IACONO's Avatar
    SAL IACONO Guest

    Default Re: arc fault and bus bar

    Thanks for the speedy input y'all !!!!!! =


  10. #10
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: arc fault and bus bar

    There is no problem with having a GFI receptacle on a circuit protected with AFCI protection.

    As was just said it is not required by code.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •