Results 1 to 31 of 31
    May 2007
    Tyler, TX
    Default Automatic Gate Opener
    Quick question regarding electrical.
    Here's the setup:
    1. Exterior automatic gate opener for a driveway
    2. Wired back to panel which goes to ground
    3. The motor is bolted to a steel frame on which the support pole is in the ground about 24"
    Is this sufficiently bonded?
    Is a GFCI breaker required?
    Any help would be appreciated. Thanks
    Bruce Thompson, Lic. #9199
    www.TylerHomeInspector.com
    Oct 2008
    Tulsa, OK
    Default Re: Automatic Gate Opener
    Not a real clear picture. An equipment grounding conductor is required to be pulled with the branch circuit.
    It may need to be GFCI protected depending on the burial depth based on 300.5.
    Ron Bibler's Avatar
    Ron Bibler Guest
    How do you known its in the ground 24'?
    How far away from the panel is the gate?
    Can you see the panel from the gate?
    May 2007
    Tyler, TX
    I don't have the clear picture either. It is being described to me by someone else.
    The grounding conductor was pulled and connected properly within the panel enclosure.
    Thanks for the 300.5 ref. I'll check it out.
    If it is on a duplex outlet, it needs GFCI. Hard wired, maybe not.
    I know of no bonding requirement for the gate or fence unless near a pool, but not a bad idea.
    May 2007
    Tyler, TX
    Owner observed it being installed
    60 ft
    I don't know
    May 2007
    Tyler, TX
    Hard wired
    Roland,
    Post the 300.5 code reference stating said requirement.
    Oct 2008
    Tulsa, OK
    Hopefully the attachment is here
    May 2007
    Tyler, TX
    I'm having trouble seeing it. Are those requirements for GFCI?
    Oct 2008
    Tulsa, OK
    I apologize--I just upgraded to office 07 and the scan function is not working so I had to cut and paste. Jerry --would you post the table 300.5 since you have the software??
    It does not lay the table out properly to copy and paste.
    Here is a screen capture of the table.
    It took me a while to figure out what you were referring to, but you are referring to the reduction in burial depth allowed with GFCI protection on residential branch circuits.
    Column 4 is what Roland is referring to.
    Oct 2008
    Tulsa, OK
    Thanks--I think I got my scanner running..
    May 2007
    Tyler, TX
    If I'm reading that right...it is saying that the assumption is that GFCI is required and the wire should be buried at 12" (the only applicable one for my situation).
    So...currently, this is not GFCI protected. I'm still confused if that is required. We'd have to install a GFCI breaker.
    What about the bonding? Any ideas there?
    Thanks for the posts.
    Oct 2008
    Tulsa, OK
    Lets see if this is clear.. You need Adobe Reader and you should be all set..
    Oct 2008
    Tulsa, OK
    Are you asking about bonding the metal gate itself? Only the motor frame is required to be bonded.
    May 2007
    Tyler, TX
    I'm asking if the motor being bolted to the steel frame is adequate.
    Quote Originally Posted by JB Thompson View Post
    No. The motor must be grounded with the equipment grounding conductor in with the circuit conductors.
    Oct 2008
    Tulsa, OK
    The motor bolted to the steel frame is enough. There is actually no code requirement to bond the gate. There may be a manufacturers requirement to bond the gate. You may have to contact them..
    No, that table is saying that, without GFCI protection, you need to follow the depths shown in Columns 1, 2, or 3 as applicable to the wiring method used. It is also saying that if you have GFCI protection installed, you can take advantage of a reduction in depth as shown in Column 4.
    That means that if direct burial cable was used, the burial depth is (All locations not specified below) 24", however, let's say they buried the cable 18" deep (such as it was planned to use PVC with a depth of 18") - BIG OOPS! - but, if GFCI protection is installed, that cable now only requires being buried 12", thus it is now okay.
    Yes, Column 4 can be used "to plan" a lesser depth, but it is most frequently used to 'correct for' an unplanned lesser depth for direct buried cable.
    After all, why use it to get to 12" if you used a method in Column 2 which only required 6" depth? There is no reduction in depth there.
    "Grounded", not "bonded"
    May 2007
    Tyler, TX
    Sorry I'm dense. Grounding aside... the motor does not have to be bonded such as pool pump motors do?
    The motor is wired with a grounding conductor that travels to the panel and thus to the driven copper rod.
    That's what I thought you were talking about - no.
    Oct 2008
    Tulsa, OK
    Well Jerry here we go--The NEC doesn't use the term grounded in regard to the motor. It uses bonded and connected, avoiding the use of the term grounded. 250.102, 250.8, 250.110 250.112, 250.119 and 250.148. About as close as they get is calling it bonded and connected.. So the motor is (according to the NEC) "bonded" to the equipment grounding conductor. So Bonded is a more correct term according to the NEC..
    From the 2008 NEC. (underlining and bold are mine)
    - VI. Equipment Grounding and Equipment Grounding Conductors
    - - 250.112 Fastened in Place or Connected by Permanent Wiring Methods (Fixed) — Specific.
    - - - (C) Motor Frames. Motor frames, as provided by 430.242.
    - - - (D) Enclosures for Motor Controllers. Enclosures for motor controllers unless attached to ungrounded portable equipment.
    - 430.242 Stationary Motors.
    - - The frames of stationary motors shall be grounded under any of the following conditions:
    - - - (1) Where supplied by metal-enclosed wiring
    - - - (2) Where in a wet location and not isolated or guarded
    - - - (3) If in a hazardous (classified) location
    - - - (4) If the motor operates with any terminal at over 150 volts to ground
    - - Where the frame of the motor is not grounded, it shall be permanently and effectively insulated from the ground.
    Roland,
    There sure are a lot of "grounded", "grounding", and "ground" terms in there regarding those motors.
    Also check the manufacturer's installation instructions for the requirement of a ground rod. Some require this:
    Oct 2008
    Tulsa, OK
    Yup--Jerry --it will be confusing until you learn to read English.. Grounded is the (past tense) end result of bonding (present continuous tense) and connecting which I was refering to.
    If you want people to think you know what you are talking about you need to learn to speak the language.
    Yup--Jerry --it will be confusing until you learn to read English.. Grounded is the (past tense) end result of bonding (present continuous tense) and connecting which I was referring to.
    Yup--Roland--it will be confusing until you learn to read ... period.
    That reference stated "groundED", "ground", and "groundING".
    We were talking about "ground", "groundED" and "groundING", and you came up with
    I know where YOUR confusion came into play, the original poster stated: (underlining is mine)
    Here's the setup:
    The correct answer is: Yes, it is "groundED", it is REQUIRED to be "groundED", that is done through the "groundING" conductor, and, no, "groundED" and "bonded" are not the same thing.
    You post here ...
    ... tried to make that connection and correction, but you had already confused yourself with your previous post.
    Which I posted the code to show you that, yes indeed, the code does use the term "groundED" in regard to the motor.
    Roland,
    Instead of trying, fruitlessly I might add, to always try to find something wrong with what I post and actually spend your efforts to try to help, your efforts would not make you look so incompetent. But trying to say you meant one thing, when you said something else, then pointing to something I said and trying to say it makes no sense, when *you said "The NEC doesn't use the term grounded in regard to the motor." and the NEC clearly does, as I pointed out "The frames of stationary motors shall be grounded " ...
    Well, the exchanges between the two of us would no longer hinder what is being done here, as I am sure most think they are.
    Learn to read, learn to type, learn to read what you type, learn to read what I type - it really is that simple - I know you can do it.
    Roland: I believe you have been earthed.
    Oct 2008
    Tulsa, OK
    I was hoping for bonding
    I'm not into bondage.