    Default Residential Lightning Protection System Grounding

    Is/Are the lightning system grounding electrode(s) allowed to be used as the required building or structure grounding electrode system?

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Oct 2008
    Location
    Tulsa, OK
    Posts
    544

    Default Re: Residential Lightning Protection System Grounding

    My answer is--only if you don't connect the lightning protection system ground rods(electrodes) to the down leads..

    OK--The real answer is no--they are separated systems but must be bonded together..250.106 (2008 ed)