    Edward Bobinchak's Avatar
    Edward Bobinchak Guest
    Default Code for drywall in garage
    In a new subdivision of single-family homes with attached garages and no second-floor or attic, the drywall on the wall adjacent to the house is fire-code and fire-taped. However, drywall on the non-adjoining walls was hung with scraps and is not taped--just but-edges. An inspector cited the the non-taped drywall as a violation saying "You are not required by code to drywall those walls, but onece you have hung it, you must tape it."
    When this citation was challenged by the builder, he was asked to show the code that says that taping is not needed. I know that code does not usually tell you what you don't need to do, but does anyone know of any source that says that taping is not necessary in this case?
    Default Re: Code for drywall in garage
    Quote Originally Posted by Edward Bobinchak View Post
    Edward: The garage walls that are not contiguous with the main house are not required by code to be covered with drywall. If they are covered with drywall the drywall is required to be taped if the AHJ says that it is. There is no code requirement that I am aware of, but the AHJ is well within his authority to require measures which exceed the adopted code.
    It is likely that JP is, even as we speak here, s-t-r-e-t-c-h-i-n-g code citations to the limit to justify taping the drywall. We'll see where it snaps . . .
    Aaron,
    Oh ye of little faith ...
    Stop and think about what you just said for a minute or two, then follow this:
    No drywall installed equals open stud spaces equals no concealed spaces.
    Install drywall and the stud space are now concealed spaces.
    What needs to be done to concealed spaces?
    Aaron,
    JP: Au contraire, I was merely patiently awaiting the bad news, never doubting it was underway.
    JP: I assume you mean:
    FIREBLOCKING.
    Building materials installed to resist the
    free passage of flame to other areas of the building through
    concealed spaces.
    Fireblocking materials include lumber; wood structural
    panels, particleboard, gypsum board, cement-based
    millboard, batts or blankets of mineral wool or glass fiber,
    or any other approved material that will resist the
    passage of flame from one concealed area to another.
    Regulated by Section R602.8 for wood-frame construction,
    fireblocking is often used to isolate vertical cavities
    such as stud spaces from horizontal concealed areas
    such as attics or floor-ceiling assemblies.
    R602.8 Fireblocking required.
    Fireblocking shall be provided
    to cut off all concealed draft openings (both vertical and horizontal)
    and to form an effective fire barrier between stories, and
    between a top story and the roof space. Fireblocking shall be
    provided inwood-frame construction in the following locations.
    1. In concealed spaces of stud walls and partitions, including
    furred spaces and parallel rows of studs or staggered
    studs; as follows:
    1.1. Vertically at the ceiling and floor levels.
    1.2. Horizontally at intervals not exceeding 10 feet
    (3048 mm).
    2. At all interconnections between concealed vertical and
    horizontal spaces such as occur at soffits, drop ceilings
    and cove ceilings.
    3. In concealed spaces between stair stringers at the top and
    bottom of the run. Enclosed spaces under stairs shall
    comply with Section R311.2.2.
    4. At openings around vents, pipes, ducts, cables and wires
    at ceiling and floor level, with an approved material to
    resist the free passage of flame and products of combustion.
    5. For the fireblocking of chimneys and fireplaces, see Section
    R1003.19.
    6. Fireblocking of cornices of a two-family dwelling is
    required at the line of dwelling unit separation.
    To restrict the movement of flame and gasses to other
    areas of a building through concealed passages in
    building components such as floors, walls and stairs,
    fireblocking of these concealed combustible spaces is
    required to form a barrier between stories and between
    a top story and the roof space. For example, the
    following locations must be firestopped in wood-frame
    construction:
    including spaces at the ceiling and floor levels.
    See Commentary Figures R602.8(1) and
    R602.8(2).
    and horizontal spaces such as soffits [Commentary
    Figure R602.8(3)], dropped ceilings
    [Commentary Figure R602.8(4)], and cove ceilings
    [Commentary Figure R602.8(5)]. Interconnections
    shown in Commentary Figure
    R602.8(6) for a bathtub installation must also be
    firestopped.
    the top and bottom of the run; see Commentary
    Figure R602.8(7).
    At openings around vent pipes, ducts, chimneys,
    and fireplaces at ceiling and floor levels
    with noncombustible materials; see Commentary
    Figures R602.8(8) and R602.8(9). Commentary
    Figure R602.8(9) illustrates fireblocking
    at chimneys and fireplaces. The fireblocking at
    ductwork would be similar
    Thanks, A.D.
    I used your reference with the inspector that didn't like the drywall and he was satisfied that the drywall in question had adequate fire blocking and did not require taping. I am not sure this would have worked with the code inspector but the report was written by the lender's agent and he bought the argument.