    Quote Originally Posted by A.D. Miller View Post
    Is an exhaust fan allowed in the ceiling of a garage with a living space above it?
    Yes, if it is ducted to the exterior and the duct is 26 gauge steel or greater, then it should comply with 309.1.1. as long as it has proper firestop caulking, etc. Also, I guess it could depend on local regulations as well.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Exhaust Fan in Garage

    Quote Originally Posted by Scott Patterson View Post
    Yes, if it is ducted to the exterior and the duct is 26 gauge steel or greater, then it should comply with 309.1.1. as long as it has proper firestop caulking, etc. Also, I guess it could depend on local regulations as well.
    Scott: It appeared to be a normal bathroom exhaust fan. I could not verify the duct type.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Exhaust Fan in Garage

    Quote Originally Posted by A.D. Miller View Post
    Scott: It appeared to be a normal bathroom exhaust fan. I could not verify the duct type.
    It would need 26 gage duct as Scott said, and I doubt that it has it. It would also need a metal exhaust hood through the exterior wall, not a plastic one which would melt and allow the duct to fall free from the exterior wall. (Because all of the plastic ones I've seen have cheapo aluminum duct the plastic cap is connected to.)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Exhaust Fan in Garage

    Quote Originally Posted by A.D. Miller View Post
    Scott: It appeared to be a normal bathroom exhaust fan. I could not verify the duct type.
    I would bet that it is not what it needs to be! I would just tell them what it should be and that you can't confirm what it is.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  6. #6
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Exhaust Fan in Garage

    Quote Originally Posted by Scott Patterson View Post
    I would bet that it is not what it needs to be! I would just tell them what it should be and that you can't confirm what it is.
    Scott and JP: Thanks. I will simply say that the installation appears to be non-compliant.


  7. #7
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Exhaust Fan in Garage

    Quote Originally Posted by A.D. Miller View Post
    Scott and JP: Thanks. I will simply say that the installation appears to be non-compliant.

    Quiter