    Default AC condensate seconday drains

    I came across this HVAC split system, and noticed that there did not appear to be a secondary condensate drain in place. Aren't both primary and secondary drains required?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: AC condensate secondary drains

    Quote Originally Posted by Ron Bishop View Post
    I came across this HVAC split system, and noticed that there did not appear to be a secondary condensate drain in place.
    Nope, sure taint one there.

    Aren't both primary and secondary drains required?
    Yep. That's why the manufacturer installed that secondary drain opening.

    Also needs a pan under the unit, unless the return is up through the bottom, in which case ... things will be a getting wet at times.

    Is that an orange extension cord in the attic being used for ... ?

    Insulation missing from that wall too.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Jeff Remas's Avatar
    Jeff Remas Guest

    Default Re: AC condensate seconday drains

    Yes required.

    No, not one there. Hope you wrote that up as a defect.


  4. #4
    Steve Miskinis's Avatar
    Steve Miskinis Guest

    Default Re: AC condensate seconday drains

    have had the pan arguement several times, I have found this wording or similiar in most installation instructions for split systems, so if not code in your area, this helps...

    The manufacturers recommend the following: “In compliance with recognized codes, it is recommended that an auxiliary drain pan be installed under all evaporator coils or units containing evaporator coils that are located in any area of a structure
    where damage to the building contents may occur as a result of an overflow of the coil drain pan or a stoppage in the primary condensate drain piping”.


  5. #5
    Join Date
    Sep 2007
    Location
    Fredericksburg, VA
    Posts
    895

    Default Re: AC condensate seconday drains

    Where is it documented that a secondary condensate line is "required"? I understand a manufacturer can illustrate a connection or recommend a connection. However, unless there is a building code in effect at the time of permit application for the installation or the manufacturer states that failure to follow their recommendations will void any warranty coverage, I do not understand why it would be classified as a defect, deficiency, or anything other than an advisory issue.

    Just to be clear, I know why one should be installed. I have a note that covers the issue in reports. I just have never seen a secondary condensate line installed anywhere.

    The above statements are expressed solely as my opinion and in all probability will conflict with someone else's.
    Stu, Fredericksburg VA

  6. #6
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: AC condensate seconday drains

    I don't know what code is in effect in your area, but this is covered in M1411.3.1 in the 2003 IRC.
    ... a secondary drain or auxillary drain pan shall be required...

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: AC condensate secondary drains

    Quote Originally Posted by Stuart Brooks View Post
    Where is it documented that a secondary condensate line is "required"? I understand a manufacturer can illustrate a connection or recommend a connection. However, unless there is a building code in effect at the time of permit application for the installation or the manufacturer states that failure to follow their recommendations will void any warranty coverage, I do not understand why it would be classified as a defect, deficiency, or anything other than an advisory issue.
    Because it is more than advisory by the manufacturer ...

    ... it is REQUIRED by the manufacturer.

    Attached is from Carrier installation instructions.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: AC condensate seconday drains

    This is from an article by Ray Moore,
    principal with Professional
    Engineering Services in Salt Lake City, ASPE vice
    president, legislative, and chair of the Utah Building

    Codes Commission Plumbing Advisory Committee.



    The
    IPC has some additional requirements for condensate drain
    pans that are not included in the UPC. Section 314 of the IPC is
    taken directly from the International Mechanical Code. Section
    314 of the IPC requires that additional protection be provided in
    case the drain line gets plugged, and the condensed water over-

    fl

    ows the drain pan and damages building components.

    The

    IPC also requires that an auxiliary or secondary drain
    system be provided. Th

    ere are four different methods for compliance.

    The fi

    rst method is to provide a secondary drain connection
    on the primary drain pan. Th

    is secondary drain must
    drain to a place where occupants would notice if a stoppage
    existed in the main drainage system. The

    second method is to
    provide a condensate drainpipe from an auxiliary or secondary
    drain pan. Th

    e third and four methods listed in the IPC require a
    water level detector and shuts of the air-conditioning equipment
    to be provided so additional condensed water is not produced.
    Typically, this water level detector is a sensor or fl

    oat switch.
    As plumbing engineers, we need to work with the mechanical
    engineers in the design of the heating and air-conditioning
    systems to provide condensate drains from the air-conditioning
    equipment.


    I did not save the link to the article but I think you can get there with
    PSDMAGAZINE.ORG

    With the duct beneath the unit, as pictured, using a float switch at the secondary condensate port would be my preferred fix. Here is a pic of float switch at recent inspection. "Unit was in utility room, on slab, no pan"




    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  9. #9
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: AC condensate seconday drains

    Quote didn't look like that on pre-view??? Don't know where all the extra returns came from but you can read it!


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: AC condensate secondary drains

    Quote Originally Posted by Vern Heiler View Post
    With the duct beneath the unit, as pictured, using a float switch at the secondary condensate port would be my preferred fix. Here is a pic of float switch at recent inspection. "Unit was in utility room, on slab, no pan"
    My preferred alternative is what used to be required in Florida, that an auxiliary drain pan was required under the unit, and when an auxiliary drain pan cannot be installed under the unit, then the auxiliary drain pan be placed beside the unit with the secondary condensate drain line running to it. Then, that auxiliary drain pan has two options (I prefer both for redundancy): 1) route the drain line from the auxiliary drain pan so it drains to a conspicuous location; 2) a shut off switch can be installed to shut the unit down.

    The reason I do not like just the shut off switch in the secondary condensate drain outlet port is, sure, it shuts the unit off, but if the coil is iced up (and we've all seen iced up coils) what happens when the unit shuts down and that ice melts into water - where does that water go? Answer: That was overflow and goes all over, damaging what you were trying not to damage. Placing the auxiliary drain pan next to the unit and piping the secondary condensate to that auxiliary drain pan gives a place where that water can go without overflowing or damaging anything.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    SAL IACONO's Avatar
    SAL IACONO Guest

    Default Re: AC condensate seconday drains

    I see alot installed with the secondary line draining in the pan. The pan then has just the float switch which I test. I've written up the lack of a drain line from the pan but got hassled from the installer on whether it is required. It appears the swtch is sufficient, but on a frozen coil with a stopped up primary drain this could lead to damage. My question is: Is a p trap required on the primary and secondary drain lines. I see alot of installs that appear to terminate at a vent with no p trap. I write them up any way because of the possibility of sewer gasses entering the controlled space. Is there code for this?


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: AC condensate secondary drains

    Quote Originally Posted by SAL IACONO View Post
    My question is: Is a p trap required on the primary and secondary drain lines. I see alot of installs that appear to terminate at a vent with no p trap. I write them up any way because of the possibility of sewer gasses entering the controlled space. Is there code for this?
    Required by the manufacturer's installation instructions.

    Code references manufacturer's installation instructions so they become "code by reference".