    Default Protection of Plastic Piping

    Are there other code references regarding this fine installation other than IRC G2415.7? I see this all the time.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Protection of Plastic Piping

    Aaron,

    That section really does not apply to what is shown in the photo.

    Go to G2415.14. (underlining is mine)

    - G2415.14 (404.14) Plastic pipe. The installation of plastic pipe shall comply with Sections G2415.14.1 through G2415.14.3.
    - - G2415.14.1 (404.14.1) Limitations.Plastic pipe shall be installed outside underground only. Plastic pipe shall not be used within or under any building or slab or be operated at pressures greater than 100 psig (689 kPa) for natural gas or 30 psig (207 kPa) for LP gas.
    - - - Exceptions:
    - - - - 1. Plastic pipe shall be permitted to terminate above ground outside of buildings where installed in premanufactured anodeless risers or service head adapter risers that are installed in accordance with that manufacturer’s installation instructions.
    - - - - 2. Plastic pipe shall be permitted to terminate with a all head adapter within buildings where the plastic pipe is inserted in a piping material for fuel gas use in buildings.
    - - G2415.14.2 (404.14.2) Connections. Connections made outside and underground between metallic and plastic piping shall be made only with transition fittings categorized as Category I in accordance with ASTM D 2513.
    - - G2415.14.3 (404.14.3) Tracer.A yellow insulated copper tracer wire or other approved conductor shall be installed adjacent to underground nonmetallic piping. Access shall be provided to the tracer wire or the tracer wire shall terminate above ground at each end of the nonmetallic piping. The tracer wire size shall not be less than 18 AWG and the insulation type shall be suitable for direct burial.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Protection of Plastic Piping

    Quote Originally Posted by Jerry Peck View Post
    Aaron,

    That section really does not apply to what is shown in the photo.

    Go to G2415.14. (underlining is mine)

    - G2415.14 (404.14) Plastic pipe. The installation of plastic pipe shall comply with Sections G2415.14.1 through G2415.14.3.
    - - G2415.14.1 (404.14.1) Limitations.Plastic pipe shall be installed outside underground only. Plastic pipe shall not be used within or under any building or slab or be operated at pressures greater than 100 psig (689 kPa) for natural gas or 30 psig (207 kPa) for LP gas.
    - - - Exceptions:
    - - - - 1. Plastic pipe shall be permitted to terminate above ground outside of buildings where installed in premanufactured anodeless risers or service head adapter risers that are installed in accordance with that manufacturer’s installation instructions.
    - - - - 2. Plastic pipe shall be permitted to terminate with a all head adapter within buildings where the plastic pipe is inserted in a piping material for fuel gas use in buildings.
    - - G2415.14.2 (404.14.2) Connections. Connections made outside and underground between metallic and plastic piping shall be made only with transition fittings categorized as Category I in accordance with ASTM D 2513.
    - - G2415.14.3 (404.14.3) Tracer.A yellow insulated copper tracer wire or other approved conductor shall be installed adjacent to underground nonmetallic piping. Access shall be provided to the tracer wire or the tracer wire shall terminate above ground at each end of the nonmetallic piping. The tracer wire size shall not be less than 18 AWG and the insulation type shall be suitable for direct burial.
    JP: Thanks, as usual.


  4. #4
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Protection of Plastic Piping

    How about this PVC used from a washer from yesterday?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  5. #5
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Protection of Plastic Piping

    Quote Originally Posted by Rick Hurst View Post
    How about this PVC used from a washer from yesterday?
    Rick: Nice job. Balch Springs?


  6. #6
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Protection of Plastic Piping

    You got it. Amazing how you picked up on that.

    rick


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •