    Default Draft/Fire Stop Foam Rated for Contact w/Flue Pipes?

    Does anybody know if the orange draft/firestopping foam is rated as being OK for direct contact with type-B flue pipes?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Draft/Fire Stop Foam Rated for Contact w/Flue Pipes?

    Quote Originally Posted by Nick Ostrowski View Post
    Does anybody know if the orange draft/firestopping foam is rated as being OK for direct contact with type-B flue pipes?

    Yes, I know that no insulation is allowed to be in contact with Type B Gas Vents.

    Not just for the insulation, it is for the vent.

    Bob Harper can explain it better than I can (because what I know about it I learned mostly from him ).

    However, I also do not see a support strap for that elbow where it turns up.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    745

    Default Re: Draft/Fire Stop Foam Rated for Contact w/Flue Pipes?

    Quote Originally Posted by Jerry Peck View Post
    However, I also do not see a support strap for that elbow where it turns up.
    Sure there is Jerry! Can't you see the romex in the backgound?

    On another thought on the "orange junk". Isn't that the type of sealant that expands with heat? If so would there be a possibility that it would expand unecessarily? Or is the rating so high before activation that the b-vent doesn't get that hot?


  4. #4
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: Draft/Fire Stop Foam Rated for Contact w/Flue Pipes?

    Yes, it is OK.......or......Yes, it is not OK?.

    If I recall correctly, something about anything being in contact with the pipe may create a hot spot because air can't flow around that flue pipe section and dissipate heat?

    There were straps on the flue pipe Jerry. They are just out of the picture to the right.


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Draft/Fire Stop Foam Rated for Contact w/Flue Pipes?

    (red bold text is mine)
    Quote Originally Posted by Jerry Peck View Post
    Yes, I know that no insulation is allowed to be in contact with Type B Gas Vents.
    Quote Originally Posted by Nick Ostrowski View Post
    Yes, it is OK.......or......Yes, it is not OK?.

    Yes, it is NOT okay.

    If I recall correctly, something about anything being in contact with the pipe may create a hot spot because air can't flow around that flue pipe section and dissipate heat?
    Yep, something like that.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: Draft/Fire Stop Foam Rated for Contact w/Flue Pipes?

    Thanks Jerry.


  7. #7
    Robert Olson's Avatar
    Robert Olson Guest

    Default Re: Draft/Fire Stop Foam Rated for Contact w/Flue Pipes?

    It's not insulation, it looks like Hilti fire stop and is approved for contact with B vent and fire blocking. It's red on application and turns orange as it ages.
    Firestop Systems - hilti.com


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Draft/Fire Stop Foam Rated for Contact w/Flue Pipes?

    Quote Originally Posted by Robert Olson View Post
    It's not insulation,
    Sure looks like that expanding foam to me.

    it looks like Hilti fire stop and is approved for contact with B vent and fire blocking. It's red on application and turns orange as it ages.
    Firestop Systems - hilti.com
    The Hilti stuff *may* be approved for use in contact with Type B gas vent, but the Type B gas vent *is not* approved to have that around it.

    I've seen and used that firestop stop before, and it does not look like that, and its purpose was not for that use either. Firestop products MUST be installed in accordance with proper firestop designs, it is not "firestop" when just applied as caulking around a Type B gas vent at a thin metal firestop plate - not unless there is a design which was approved for its use there (and any construction requiring firestopping for a Type B gas vent would have the vent in a shaft, which would be the firestopping, and the vent would not be firestopped as shown, would not be any need to, the shaft is the separation and firestop.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Exclamation Re: Draft/Fire Stop Foam Rated for Contact w/Flue Pipes?

    Robert, that link is only to Hilti's entire product line, which narrows it down to about 50,000 items. Can you be a little more specific about which Hilti product you are referencing? Thx

    In general, you cannot seal any listed firestop unless it is permitted by the listing and the product is specified. For instance, If you seal the listed firestops on air cooled factory built wood burning fireplaces, you stop cooling the chase, which raises temps. and voids the listing. Some gas fireplaces, such as Heatilator, Heat&Glo, Quadrafire actually have tested their firestops caulked with 300*F rated RTV silicone and approved it. What they did not approve is a big blob of 'stuff' at the firestop where, as Nick mentioned, you will raise the temps. and threaten your clearances. You also need to be concerned with odors and off-gassing.

    I recommend as an inspector, you record the make, model and serial number of the appliance, mfr. and model of the venting and contact the mfr.s. In the case with a B-vented gas fireplace, I would contact both mfrs. If they say no but the caulking mfr., such as Hilti approve it, then there is a transfer of liability to Hilti or an assumption of the risk on their part and that of the installer. This becomes a problem in commercial work where you exceed three floors and come under the IBC and have fire rated assemblies. In general, they want to see firestops listed to UL 814 for the hose stream test. Again, contact the mfrs.


    HTH,
    Bob

    Keep the fire in the fireplace.