    Default CHIMNEY STACK ON ROOF

    inspected this home in colorado today and wood burning chimney was on north roof. it was two feet above north roof,but south roof was quite abit higher and there were bedroom windows thaT opened toward that chimney. is this correct or should it be also above south roof.hots attached

    charlie

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: CHIMNEY STACK ON ROOF

    Looks fine to me according to the schematic.


  3. #3
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Default Re: CHIMNEY STACK ON ROOF

    It's a foot too short at the very least. All chimneys must be at least 3 ft above the roof regardless.

    If the nearby taller roof is more than 10 ft. away, then it would not have to be taller according to the code. It may need to be taller if there is an adverse wind effect or they need the additional height to overcome house stack effect. Keep in mind that this additional chimney is exposed and thus will cool down quickly so you don't want to over do it and make it too tall. You reach the point of diminishing return rather quickly.
    HTH,
    Bob

    Keep the fire in the fireplace.