Results 1 to 6 of 6
  1. #1
    Join Date
    Mar 2007
    Location
    Atlanta, Georgia
    Posts
    1,088

    Default Proper Support for Thermal Expansion Tank

    IRC 2903.4 requires the use of a thermal expasion tank. I am not able to find any verbiage about the proper secureing and support of said tank.

    Almost every picture of a tank on this forum gets bashed for improper support. Yeah, I know it makes sense but is there some specific mention of how or a requirement to do so?

    It is "not right" and "common sense" but I want to back up my claims with code or manufacturers instructions if I get in a discussion with the builder/plumber. Any pointers?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    "The Code is not a peak to reach but a foundation to build from."

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Proper Support for Thermal Expansion Tank

    Quote Originally Posted by Bruce Ramsey View Post
    IRC 2903.4 requires the use of a thermal expasion tank. I am not able to find any verbiage about the proper secureing and support of said tank.

    Almost every picture of a tank on this forum gets bashed for improper support. Yeah, I know it makes sense but is there some specific mention of how or a requirement to do so?

    It is "not right" and "common sense" but I want to back up my claims with code or manufacturers instructions if I get in a discussion with the builder/plumber. Any pointers?
    With the copper pipe and as pictured I don't see the need for additional support. Most of what I'm seeing now are PEX pipe with dangling expansion tanks, those need support.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Proper Support for Thermal Expansion Tank

    As Scott said, with copper pipe and being mounted vertically above (or below) it ... that is the key.

    When mounted off to one side, the weight of the tank and the water in the tank can break the fittings off and then additional support would be required, same goes for PEX systems - additional support would be required.

    By the way, I am sure you already have this, but that insulation needs to be 6" or more from the draft hood.

    The Watts installation instructions even shows it self-supported vertically above or below the rigid piping, and additionally supported when teed off other than vertically above or below: http://www.watts.com/pdf/1915356.pdf

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Nov 2007
    Location
    Chicago
    Posts
    548

    Default Re: Proper Support for Thermal Expansion Tank

    That is the proper way with copper pipe. If it was plumbed to the side then additional support is needed. You can go by the manufactures instructions. Here is a PDF from Watts http://www.watts.com/pdf/1915356.pdf


  5. #5
    Join Date
    Nov 2007
    Location
    Chicago
    Posts
    548

    Default Re: Proper Support for Thermal Expansion Tank

    Wow I just noticed Jerry already posted the link. Helps if I refresh my Cache.


  6. #6
    Join Date
    Nov 2007
    Location
    Chicago
    Posts
    548

    Default Re: Proper Support for Thermal Expansion Tank

    Oh the water shut off is in the wrong spot. Most plumbing codes want the shut off to be before the the tank. This part is from the Illinois Plumbing Code.

    C) A properly sized and approved expansion tank shall be located on the outlet side of the check valve in the water heater's cold water supply with no shut-off valve between the heater and expansion tank.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •