Results 1 to 2 of 2

Thread: Ground clamps

  1. #1
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Ground clamps

    The attach picture shows multiple ground conductors spliced with ground clamps.

    The copper ground conductor for the main service equiipment is spliced and has a clamp. The secondary copper conductor which is also clamped is for copper pipe bonding connection. The aluminum wire is the grounding conductor for the adjacent panel.

    Questions:

    1. Can you use a spliced connection for service equipment ground conductors?
    2. Can an adjacent panel be grounded as shown (clamped aluminum conductor) outside of the main service equipment?

    Thanks

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Ground clamps

    Quote Originally Posted by Ken Amelin View Post
    The attach picture shows multiple ground conductors spliced with ground clamps.

    The copper ground conductor for the main service equipment is spliced and has a clamp. The secondary copper conductor which is also clamped is for copper pipe bonding connection. The aluminum wire is the grounding conductor for the adjacent panel.

    Questions:

    1. Can you use a spliced connection for service equipment ground conductors?
    2. Can an adjacent panel be grounded as shown (clamped aluminum conductor) outside of the main service equipment?

    Thanks
    The grounding electrode conductor (the main one from the service equipment to the grounding electrode) is not allowed to be spliced LIKE THAT. The splice is required to be an irreversible compression connector or exothermically welded together.

    Others are allowed to be connected to the grounding electrode conductor, but only with proper clamps. The split bolt clamp may work if it is rated for both copper and aluminum, the others are not rated for that purpose - they are "pipe clamps" which are rated to go on "pipes".

    The acorn type clamp at the grounding electrode is okay as long as it is installed correctly (looks like it might be in the photo but it is hard to see in the photo).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •