    Default Water heater tied to plug-in 220 outlet

    I am sure this is not right but where does it say a water heater has to be hard-wired and cannot use a 220 dryer type outlet ?

    Gene

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Water heater tied to plug-in 220 outlet

    NEC (bold is mine)
    - 400.7 Uses Permitted
    - - (A) Uses. Flexible cords and cables shall be used only for the following: (not in there)
    - 400.8 Uses Not Permitted
    - - Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following: (as stated above - not in 400.7, and not in 400.8 either)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Apr 2008
    Location
    McKinney Texas
    Posts
    501

    Default Re: Water heater tied to plug-in 220 outlet

    Jerry, thanks, I am super behind tonight on inspection paperwork. Appreciate you checking this for me or confirming what I thought was right.