05-22-2009, 11:13 AM #1
Maximum height for main disconeect
Is there a maximum height for the main shut off in a panel? Not the panel height itself, but the main disconnect. I have one at around 78-80". Thanks for your replies ahead of time.
Jody
Similar Threads:
-
05-22-2009, 11:34 AM #2
Re: Maximum height for main disconnect
Jody,
The maximum height of the handle is 6'7" (79") above the floor of the working space. It used to be 6'8" (80").
And that is not to "center" of the breaker, that is to the handle "when in its highest position".
-
05-22-2009, 12:40 PM #3
Re: Maximum height for main disconeect
Thanks Jerry.