    Default Maximum height for main disconeect

    Is there a maximum height for the main shut off in a panel? Not the panel height itself, but the main disconnect. I have one at around 78-80". Thanks for your replies ahead of time.

    Jody

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Maximum height for main disconnect

    Jody,

    The maximum height of the handle is 6'7" (79") above the floor of the working space. It used to be 6'8" (80").

    And that is not to "center" of the breaker, that is to the handle "when in its highest position".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com