Results 1 to 10 of 10
  1. #1
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Multiple conductors at GE THQL Breaker?

    Anyone know if these are listed for 2 conductors - I can't find the specs at the GE site.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Michael Thomas; 06-09-2009 at 06:10 PM.
    Crawl Space Creeper
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Multiple conductors at GE THQL Breaker?

    I've never seen terminals like those rated for more than one wire.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Multiple conductors at GE THQL Breaker?


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Multiple conductors at GE THQL Breaker?

    Quote Originally Posted by Bill Kriegh View Post

    Bill,

    I'm not following that "Wire Size" column.

    Certainly that is not the "number of wires allowed per terminal" as, for example the first line of that table, you would not be allowed to run 2 #12 in parallel for that air conditioner. Or the second line of 3 #12 in parallel for each terminal or 6 #12 going to that 20 amp double pole breaker.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Multiple conductors at GE THQL Breaker?

    The attached is from the next page after what Bill posted and shows the wire sizes allowed.

    Only one conductor per terminal.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Multiple conductors at GE THQL Breaker?

    Apologies. Got interrupted and extracted the wrong page.


  7. #7
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Multiple conductors at GE THQL Breaker?

    Thanks to you both.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Multiple conductors at GE THQL Breaker?

    Bill,

    Still trying to figure out what the "Wire Sizes" on that first table are supposed to indicate - do you have any information on what that is saying?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Multiple conductors at GE THQL Breaker?

    The page has mistakes. Where it says 2#12 it should say 2-12, meaning sizes from AWG 2 to AWG 12.

    GE rates the lugs on the breakers for a single conductor, no exceptions.

    Dunno when the catalog will get fixed.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Multiple conductors at GE THQL Breaker?

    Quote Originally Posted by Bill Kriegh View Post
    The page has mistakes. Where it says 2#12 it should say 2-12, meaning sizes from AWG 2 to AWG 12.

    GE rates the lugs on the breakers for a single conductor, no exceptions.

    Dunno when the catalog will get fixed.

    Now that page makes sense. Thank you.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •