    Atlanta, Georgia
    Default Minimum Interior Door Opening Size
    IRC specifies that the main egress door must be 3' wide and 6'8" tall, hinged on one side. But I could not find any minimums regarding interior doors or doors to bathrooms.
    16 year old house. Half bath is located under stairway. As a result the stairs intrude into the path of the door way. Dumb design. There is a pantry closet to the right of the bathroom that could be sacraficed to allow the bath to expand so the door could be relocated and would not be blocked by the stairs. Anyway...
    Are there any IRC references to the minimun opening size to interior rooms, the size of doorways, or access to bathrooms?
    A.D. Miller's Avatar
    A.D. Miller Guest
    Default Re: Minimum Interior Door Opening Size
    SECTION R305
    CEILING HEIGHT
    R305.1 Minimum height. Habitable rooms, hallways, corridors,
    bathrooms, toilet rooms, laundry rooms and basements
    shall have a ceiling height of not less than 7 feet (2134 mm).
    The required height shall be measured from the finish floor to
    the lowest projection from the ceiling.
    Exceptions:
    1. Beams and girders spaced not less than 4 feet (1219
    mm) on center may project not more than 6 inches
    (152 mm) below the required ceiling height.
    2. Ceilings in basements without habitable spaces may
    project to within 6 feet, 8 inches (2032 mm) of the finished
    floor; and beams, girders, ducts or other
    obstructions may project to within 6 feet 4 inches
    (1931 mm) of the finished floor.
    3. For rooms with sloped ceilings, at least 50 percent of
    the required floor area of the room must have a ceiling
    height of at least 7 feet (2134 mm) and no portion of
    the required floor area may have a ceiling height of
    less than 5 feet (1524 mm).
    4. Bathrooms shall have a minimum ceiling height of 6
    feet 8 inches (2036 mm) over the fixture and at the
    front clearance area for fixtures as shown in Figure
    R307.1. A shower or tub equipped with a showerhead
    shall have a minimum ceiling height of 6 feet 8 inches
    (2036 mm) above a minimum area 30 inches (762
    mm) by 30 inches (762 mm) at the showerhead.
    [1]Minimum ceiling heights are required for habitable
    rooms hallways, corridors, bathrooms, toilet rooms,
    laundry rooms and basements. The minimum required
    height of 7 feet (2134 mm) helps maintain a healthy interior
    environment. The dimension must be measured
    to the lowest projection from the ceiling.
    For ceilings having exposed beams that project
    down from the ceiling surface, the ceiling beam members
    may project no more than 6 inches (152 mm) below
    the required ceiling height, provided the beams or
    girders are placed at no less than 4 feet (1219 mm) on
    center. Basements need have a ceiling height of only 6
    feet, 8 inches (2033 mm) or more, with at least 6 feet, 4
    inches (1932 mm) of clear height under beams, girders,
    ducts and similar obstructions.
    For rooms with sloped ceilings, the code requires
    only that the prescribed ceiling height be maintained in
    one-half the area of the room. However, no portion of
    the room that has a ceiling height of less than 5 feet
    (1524 mm) must be used in the computations for minimum
    floor area.
    Exception 4 defines the required minimum ceiling
    height over toilet, bath and shower fixtures. This
    exception would allow a sloping ceiling over toilet, bath
    or shower fixtures if the minimum ceiling height of 6
    feet, 8 inches (2036 mm) is maintained over the fixture
    and at the front clearance area.
    Atlanta, Georgia
    Thanks for the quick response.
    In reading through I did not see any specific reference to doorways but there were numerous references to 6'8" and access. Looks like a combination of factors, 50% of floor space, clearance in front of fixture, etc.
    I wrote it up as a skull buster.
    A.D. Miller Guest
    BR: It is definitely that. I always mention the liability issues with such things. Gets the ball rolling quickly.
    Healdsburg, CA
    I don't know of a code that stipulates interior door sizes, minimum or maximum width other than the main entry door, which is an exterior door? However, the common size besides the 6'-8" height; bedroom doors 2'-8" width, random closet 2'-6", and bathrooms 2'-4". You may want to point out that low doors present a hazard to foot traffic, but that would seem fairly obvious to the even less than alert home buyer.
    "Your honor, I smacked my head on entering a small closet under the stair and I think I’m entitled to an award because I wasn't told it was below normal height." Judge: "Next case?"
    Jerry McCarthy
    I called it a "head banger" 'over there'.
    Atlanta, Georgia
    Written in ICC parlance:
    "The minimum required height of 7 feet (2134 mm) helps maintain a healthy interior environment."
    Apr 2008
    Massachusetts
    IRC says:
    R311.4.2 Door type and size.
    The required exit door shall be a side-hinged door not less than 3 feet (914 mm) in width and 6 feet 8 inches (2032 mm) in height. Other doors shall not be required to comply with these minimum dimensions.
    I believe that the old BOCA code required a minimum of 2'-6" for all other interior doors and 2'-0" for bathrooms. A BOCA instructor years ago told me that the logic for 2'-0" was that bathrooms usually don't have a lot of people in them, and "if you can get in, then you can get out". I don't know why the 2'-6" is not in IRC. Practically speaking, I don't know why anyone would build a room with a smaller door. It would be tough to get furniture in and out.
    IBC has a 32" minimum door width.
    1008.1.1 Size of doors.
    The minimum width of each door opening shall be sufficient for the occupant load thereof and shall provide a clear width of not less than 32 inches (813 mm).
    There are several exceptions to the 32" requirement.
    Ridgewood, NJ
    I thought the minimum interior door opening changed to 32" with the Americans with Disabilities Act in the late 80's or early 90's.
    A.D. Miller Guest
    NL: Even if, ADA does not apply.
