Results 1 to 6 of 6
  1. #1
    Tony Dziabuda's Avatar
    Tony Dziabuda Guest

    Default Question about service drop and window

    Hello all,
    My first post and question here.
    I know that a service drop can't be located within 3" of a window, but what if it's a fixed picture window? Does that still apply?

    I appreciate all the knowledge available to me from this site. Thanks.

    Tony

    Similar Threads:
    Member Benefits1

  2. #2
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Question about service drop and window

    Quote Originally Posted by Tony Dziabuda View Post
    Hello all,
    My first post and question here.
    I know that a service drop can't be located within 3" of a window, but what if it's a fixed picture window? Does that still apply?

    I appreciate all the knowledge available to me from this site. Thanks.

    Tony
    TD: I think you meant 3' and not 3". The rule applies to operable windows, and not fixed pane units.


  3. #3
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Question about service drop and window

    Here's the applicable code:

    230.9 Clearances on Buildings.
    Service conductors and final spans shall comply with 230.9(A), (B), and (C).
    (A) Clearances. Service conductors installed as open conductors or multiconductor cable without an overall outer jacket shall have a clearance of not less than 900 mm (3 ft) from windows that are designed to be opened, doors, porches, balconies, ladders, stairs, fire escapes, or similar locations.
    Exception: Conductors run above the top level of a window shall be permitted to be less than the 900-mm (3-ft) requirement.


  4. #4
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Question about service drop and window

    "230.9 Clearances on Buildings.
    Service conductors and final spans shall comply with 230.9(A), (B), and (C).
    (A) Clearances. Service conductors installed as open conductors or multiconductor cable without an overall outer jacket ..."


    That's odd, if I remember correctly, a cable is defined as;
    2 or more conductors with an insulating overall outer jacket.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  5. #5
    Tony Dziabuda's Avatar
    Tony Dziabuda Guest

    Default Re: Question about service drop and window

    Yep, meant 3'. Thanks for the replies, that's what I thought.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Question about service drop and window

    Quote Originally Posted by Rick Cantrell View Post
    "230.9 Clearances on Buildings.
    Service conductors and final spans shall comply with 230.9(A), (B), and (C).
    (A) Clearances. Service conductors installed as open conductors or multiconductor cable without an overall outer jacket ..."

    That's odd, if I remember correctly, a cable is defined as;
    2 or more conductors with an insulating overall outer jacket.

    First, the outer jacket is not "insulating", it is for "protection", and, yes, you can have cable with or without an overall outer jacket.

    The service drop cable you see is multiconductor cable without an overall outer jacket, NM cable is multiconductor cable with an overall outer jacket.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •