    Stephen G Sheldon's Avatar
    Stephen G Sheldon Guest
    Default Is duct insulation considered a combustible
    In a crawl space the furnace vent passes along side and touches an insulated duct vent. Should I call this out or Is this acceptable?
    Default Re: Is duct insulation considered a combustible
    Quote Originally Posted by Stephen G Sheldon View Post
    SS: Acceptable, though the slightest possibility exists for developing a "hot spot" in the vent at the pooint of contact with the insulation.
    Stephen,
    NOT ACCEPTABLE.
    Forget the part about being combustible or not, no insulation is allowed within the stated clearance either.
    Last edited by Jerry Peck; 07-27-2009 at 10:59 AM. Reason: typo Aaron pointed out.
    Stephen,
    NOT ACCEPTABLE.
    Forget the part about being combustible or not, not insulation is allowed within the stated clearance either.
    JP: Which part of the insulation in question is combustible at those termperatures?
    Aaron,
    Did you not read what I posted and you quoted?
    Exclamation Six issues here
    The duct wrap does not meet ASTM E-136 so therefore it should be treated as "combustible" inspite of our own personal perception of the material.
    The insulation is not only invading in the stated clearance space but is in direct contact. This blocks the flow of cooling air and creates a hot spot.
    The point where the insulation is in contact is obscured from normal inspection. A bad spot could develop there undetected. This is why the codes and stds. do not allow covers or wrapping of vent connectors. B-vent and L-vent, being listed systems with a proven track record are allowed as connectors even though their outer skin prevents direct visualization of the flue lining. You still must maintain the clearance to their outer skin per their listing.
    Practically speaking, all that heat against that insulation may release either formaldehyde or phenol resins, both of which are nasty, stink and carcinogens.
    The 'foil' scrim you see is actually FSK--foil scrim kraft, otherwise known as brown paper wrapped in tin foil. It carries a flame spread of 25 but IS combustible.
    Should not be using single walled vent connector in a crawl space.
    Any more pics?
    Bob
    JP: I did, but what does this mean?:not insulation is allowed within the stated clearance either
    Default Re: Six issues here
    [quote=Bob Harper;93633]The duct wrap does not meet ASTM E-136 so therefore it should be treated as "combustible" inspite of our own personal perception of the material.
    BH: As a fire espert you are certainly aware that anything is combustible with enough heat applied to it.
    BH: That is what I said.
    The point where the insulation is in contact is obscured from normal inspection. A bad spot could delelop there undetected. This is why the codes and stds. do not allow covers or wrapping of vent connectors. B-vent and L-vent, being listed systems with a proven track record are allowed as connectors even though their outer skin prevents direct visualization of the flue lining. You still must maintain the clearance to their outer skin per their listing.
    BH: Good point. Hadn't consdered that.
    BH: Maybe.
    Typo:
    "not insulation is allowed within the stated clearance either"
    Should be:
    "no insulation is allowed within the stated clearance either"
    Which means that if that is single wall - no insulation is allowed within the 6" minimum clearance.
    For Type B gas vents that clearance is 1" with no insulation allowed within that clearance.
