    Default TPRV drain pipe on Tankless water heater

    Tankless gas water heaters are becoming more popular in my area and I am wondering if the termination height standards for the TPRV pipe are the same?

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: TPRV drain pipe on Tankless water heater

    Quote Originally Posted by Mike Birenbaum View Post
    Tankless gas water heaters are becoming more popular in my area and I am wondering if the termination height standards for the TPRV pipe are the same?
    Yes, the termination height if a factor of the most restrictive of all the following: 1) the code (not more than 6" above the floor, ground or receptor); 2) the manufacturer of the T&P valve (at least 6" above the floor, ground, or receptor); and 3) the manufacturer of the tankless water heater (does not matter what they say, between 1) and 2) you are left at 6" above exterior grade ).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com