    Default Boiler clearance

    Too late for Burnham, Anyone have the clearance requirements for boiler sidewall.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Boiler clearance

    I'm too lazy to look up the Boiler clearances per Manuf. I just tag'em for lack of fire separation. 1/2 hour in SF, 1 hour in 1-4 multi-unit in the City. Easy for me, easy for others to understand.
    In this case, looks like you have around 2-3". That might be enough per Manuf. on a newer boiler like that, not me though. Did you take the cover off? Lots of times there's a clearance tag inside on a panel.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  3. #3
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: Boiler clearance

    no didn't remove the cover.


  4. #4
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Exclamation Re: Boiler clearance

    You have clearances to combustibles then you have practical service and inspection clearance. If you cannot get to every *thing* on the boiler and appurtenances, then it's too close. For instance, if the rating plate is on the left side of the boiler housing, then it is too close to access for reading.

    Measure from the single walled vent connector: 18" clearance to combustibles unless reduced clearance stated by mfr.

    I want to see you replace that PRV without cussing someone.

    Keep the fire in the fireplace.

  5. #5
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: Boiler clearance

    Thankyou all. And Bob, Nice simple description, thanks.