Results 1 to 15 of 15
Thread: Loose breaker
    Donn Lindorfer's Avatar
    Donn Lindorfer Guest
    Default Loose breaker
    Heh gang my 1st time posting on the board. Just 2 easy questions. The pictures below look to me like a loose breaker. Just looking for some confirmation. The panel and breakers are Square D. Also, the main risk is arcing which is a fire danger, not to mention a loose breaker can also be a shock risk. Any other risks you would call out?
    Secondly, this same panel has a cable wire grounded to a screw on the cover of the box. Please correct me if I am wrong, but I do not believe this allowed, correct?
    Thanks!!
    Default Re: Loose breaker
    You got the double tapped breakers and the white conductors noted also I guess.
    Yes, got the double tap, but not the white conductor. The white conductor is connected to a terminal labeled "load neutral" which is ok, right? I believe this circuit is for a 220 hot tub.
    Quote Originally Posted by Donn Lindorfer View Post
    The white is on a GFCI breaker. Look closely and you will see the Test button.
    Yeah, that loose breaker could be a problem - it could also be an easy fix ... if it has not already arced up the breaker tab, if it has that would be bad news. However, I am guessing that the panel is a CTL panel and that lower right breaker simply cannot be fit on properly, and there is a reason for that ... it is the wrong breaker in the wrong panel.
    You got the double tapped breakers and the white conductors noted also I guess. rick
    He got you there Rick!
    That loose breaker is not even a Sq D breaker, which is why it is not fitting correctly.
    Apr 2009
    NY State
    Jerry, your first instinct was correct. Take a closer look. It is a SqD. Might be counterfeit though as it does not look typical.
    My bet is that it is a CTL board where someone tried to use a twin breaker.
    Cable companies ground to where ever they want it seems, valid or not. Using a cover screw is not a listed application which is why they've come up with some strange contraptions to clamp onto panel boxes.
    Peter,
    My second post was adding to my first post.
    I think that is a non-CTL breaker in a CTL panel, AND, that breaker is not a Square D.
    The reason I say it is not a Square D is the width or the raised part, compare it to the Square D breaker opposite it - there is no way that divider piece is going to fit between the non-Square D breaker and the Square D breaker above it as the width of the raised part is the full width of the breaker, unlike the other Square D breakers.
    See what I am referring to?
    South-West Michigan
    Post Re: Loose breaker
    I don't know, Jerry. I was thinking the same thing, but look at this:
    HomeLine ® Circuit Breakers - Schneider Electric United States
    I would tend to agree that it is either improperly installed, or not made for the panel it is installed in. This may be due to the breaker being a mini or tandem.
    Randall Aldering GHI BAOM MSM
    Housesmithe Inspection
    www.housesmithe.com
    South-West Michigan
    This will save looking it up on the web site.
    www.housesmithe.com
    Apr 2009
    NY State
    Yes, that is definitely a SqD breaker.
    You can clearly make out the "D in a square" on the sticker.
    On The Mason-Dixon Line
    square D Homeline breaker in a Square D QO panel
    Apr 2009
    NY State
    That's physically impossible.
    Besides, that is an HOM panel.
    my bad !
    I guess thats what I get for looking at it with that stupid laptop instead of my desktop
    Well ... I would not say "clearly make out", I had to zoom in and squint but then I saw the D.
    Thus I stand (sit) corrected.