Results 1 to 3 of 3

Thread: Fire Block?

  1. #1
    Anthony Alderman's Avatar
    Anthony Alderman Guest

    Default Fire Block?

    If you convert a single family home into a duplex do you have to put a fire wall in the attic and crawl?? It's a remodel. Agent asked me

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Fire Block?

    Quote Originally Posted by Anthony Alderman View Post
    If you convert a single family home into a duplex do you have to put a fire wall in the attic and crawl?? It's a remodel. Agent asked me
    I had this come up last year and when I looked into it I found that it all depends on the AHJ for the area. In my town they only require firewalls if there it is a 4-plex or more. Down the road 10 miles in the town of Franklin they require a firewall on any multi-family building.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Fire Block?

    The IRC code requires it to separate occupancies and dwelling units, then (as I recall) allows an exception for one- and two-family dwellings, with a duplex being a two-family dwelling.

    That would mean three or more, yes.

    As Scott said, though, your local AHJ may require it for duplex, used to be required in South Florida until the Florida Building Code went into effect which is based on the ICC codes.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •