    Default Unknown Flue Pipe

    In a house built in 2001 there is a gas furnace that is properly connected, but to the side of it is are two larger flue pipes (only one is shown in the picture) vented through the ceiling but which are open on the bottom. Can anyone comment on what this may be about?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Unknown Flue Pipe

    Combustion air as that space was a "confined space" and those vents were installed to make up the difference.

    One should be within 12" of the ceiling (that one looks more than 12" down) and one should be within 12" of the floor.

    Size also matters as those are required to be 100 square inches minimum - what diameter were those vents? Need to be 12" minimum diameter for 100 square inches.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Stephen G Sheldon's Avatar
    Stephen G Sheldon Guest

    Default Re: Unknown Flue Pipe

    jerry,

    Thank you. That makes alot of sense now that I think about it.