    I have read the post about doubled lugged neutrals and nuetral and ground wires sharing a common terminal. Please take a look at this photo and share your thoughts. Cite relate code so I can do further investigation. Thanks for your help.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Another Neutral and ground Question

    The NEC requires things to be installed per manufacturer's instructions. The size and number of wires permitted in the lug shown should be listed on the label inside the panel. If the info is absent from the panel it can usually be be gleaned from an online catalog.

    2008 NEC®©
    110.3 Examination, Identification, Installation, and Use
    of Equipment.
    (B) Installation and Use.
    Listed or labeled equipment
    shall be installed and used in accordance with any instructions
    included in the listing or labeling.




  3. #3
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Another Neutral and ground Question

    The conductors are way unequal in size. The lug is not rated for two wires even if they were equal.
    That looks like a main neutral lug with a branch circuit ground tucked in.
    It is three times wrong.