    Default Electrical Gutter Boxes

    I did a 4-plex today.

    The end of the gutter box that contains the service entrance conductor connection with the house conductors is about 2 feet from a gas meter.

    Panels shouldn't be within 3 feet of the gas meter, what about the gutter boxes?

    bm

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Electrical Gutter Boxes

    Quote Originally Posted by brianmiller View Post
    Panels shouldn't be within 3 feet of the gas meter, what about the gutter boxes?

    Brian,

    That panels are not allowed within that space as they contain ignition sources - the breakers, fuses, etc.,

    The wire gutter is not a problem as it does not contain ignition sources, only wiring and connectors.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com