Thread: Service entrance neutrals
-
10-02-2009, 12:04 PM #1
Service entrance neutrals
Does anyone know if it is permissible to secure a neutral from a breaker at the service entrance box with the main service entrance neutral?
Thanks,
Ryan
Similar Threads:
-
10-02-2009, 01:30 PM #2
Re: Service entrance neutrals
Something is very wrong here. First of all neutrals don't connect to breakers. Secondly, what is the purpose of this? Thirdly, I believe that lug is only rated for 1 conductor. This service needs to be corrected by a qualified electrician.
-
10-02-2009, 01:35 PM #3
Re: Service entrance neutrals
"First of all neutrals don't connect to breakers."
Execpt for AFCI / GFCI breakers, and looking at the twist in the wire, it could be.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
10-02-2009, 01:38 PM #4
Re: Service entrance neutrals
OK, that never entered my mind. If thats the case the connection should be to the neutral bar, of course.
-
10-02-2009, 01:50 PM #5
Re: Service entrance neutrals
If, as the OP stated, that is the SE, then the grounds and neutrals are on the same buss. But the neutral should be under a lug by itself.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
10-02-2009, 04:37 PM #6
Re: Service entrance neutrals