    Situation... Two #12 wires connected to one 40 amp breaker. I call it out on the report as two wires on a single over sized breaker recommend replacing with two 20 amp breakers by a licensed electrician.

    Listing agent calls me this morning.... "#12 wire is for 20 amps, I looked it up this morning. 20 amp and 20 amp is 40 so the one breaker is good. duh! Can't you even do math? How dumb are you? I need you to take it off the report and resend the report the buyer so they will stop asking for the repair"

    Yeaaa... that's going to happen. I didn't even bother explaining. URG

    Similar Threads:
    OREP Insurance

  2. #2
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: How dumb am I....

    How dumb are you?
    KR: I don't know, but standing up with a fish in front of you and smiling like you had good sense is not a good sign.


  3. #3
    K Robertson's Avatar
    K Robertson Guest

    Default Re: How dumb am I....

    Quote Originally Posted by A.D. Miller View Post
    KR: I don't know, but standing up with a fish in front of you and smiling like you had good sense is not a good sign.
    And this coming from a guy with a koi pond.... hmmmmm


  4. #4
    Michael Greenwalt's Avatar
    Michael Greenwalt Guest

    Default Re: How dumb am I....

    and I thought the only math they knew was $$$Sales x %%%% = Commission. I think they are improving.


  5. #5
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    745

    Default Re: How dumb am I....

    Sure they can use it! Tell them to get a hacksaw and cut it in 1/2!


  6. #6
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: How dumb am I....

    Quote Originally Posted by K Robertson View Post
    And this coming from a guy with a koi pond.... hmmmmm
    KR: Good point.


  7. #7
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: How dumb am I....

    A conductor cannot be connected in paralell unless it is 1/0 or larger. See 2005 NEC 310.4.


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: How dumb am I....

    Quote Originally Posted by Rollie Meyers View Post
    A conductor cannot be connected in paralell unless it is 1/0 or larger. See 2005 NEC 310.4.

    Also, the only way these would be in parallel would be if they both went to the same thing, and that is highly unlikely.

    Plus, there are other requirements for parallel conductors other than just that minimum size of 1/0.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: How dumb am I....

    Quote Originally Posted by Jerry Peck View Post
    Also, the only way these would be in parallel would be if they both went to the same thing, and that is highly unlikely.

    Plus, there are other requirements for parallel conductors other than just that minimum size of 1/0.
    It failed just on that point.