    Colorado Springs, CO
    Default A/C Condensate Drain Connected To Waste Piping
    Anything wrong with connecting the A/C condensate drain directly to the waste piping as seen in the attached photos?
    Bruce Breedlove
    www.avaloninspection.com
    Default Re: A/C Condensate Drain Connected To Waste Piping
    delete
    Last edited by Bruce Breedlove; 10-14-2009 at 06:17 PM. Reason: corrected photo mistake in original post
    Bruce Breedlove
    Yep, it must be an indirect connection. You don't want the nasties from the sewer from the sewer to migrate to the air stream.
    Jim,
    Wouldn't the trap stop the sewer gasses from flowing up the pipe?
    Bruce Breedlove
    It's not just gases, think bacteria and legionnaire's disease.
    Plus that trap is not vented, is a running trap, and will likely dry out during the off season.
    OK, thanks. Time to send out a revised report.
    Bruce Breedlove
    Bruce,
    That trap is not stopping anything.
    That is a site built "running trap" and running traps are prohibited. Also looks like it might be longer than 4 feet and PVC is required to be supported every 4 feet. Plus, you would want a support at that 90 change from vertical to horizontal to 90 degreed horizontal, otherwise the fittings could break.
    Brad Deal's Avatar
    Brad Deal Guest
    Bruce,
    This is called a "cross connection." If the sewer line backs up, sewer water will be forced into the condensate drain and into the condensate pan. Black water is now in direct contact with the air we breath, vented throughout the living space. This is akin to an overflowed toilet inside the HVAC system.
    This is a health safety hazard.
    Brad Deal
    Message received and understood. Client has been sent a revised report.
    Thanks for the assistance and education.
    Bruce Breedlove
