    Default Electrical running through supply duct

    As far as I know this is illegal. This area is located in a closet. Any thoughts?

    Thanks,

    Ryan

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Electrical running through supply duct

    That is probably running to a damper of some type which is operated remotely, with those supplying power to it. That is, unless you also saw those coming out the top side of the duct.

    By the way, that duct is not supported properly either.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Ryan Stouffer's Avatar
    Ryan Stouffer Guest

    Default Re: Electrical running through supply duct

    I am almost certain it is not running to a damper. Is it allowed? To my knowledge it is not.


  4. #4
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Electrical running through supply duct

    Ryan
    Electric wires running through or in ducts or plenums must be rated for use in a plenum. In fire alarm systems we call it "Plenum wire" and "Fire wire".
    I don't know if regular old romex is rated for that or not, but I dought it.
    Plenum Wire and Cable FAQs from Allied Wire and Cable - Manufacturer and Distributor of Plenum Wire and Cable#

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.