    I don't see where this panel is bonded. I know you guys will set me straight. It is a AC subpanel.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: Help

    what is green and is found in a panel?


  3. #3

    Default Re: Help

    What Wayne said. It does look like you're missing a wire clamp though.


  4. #4
    Join Date
    Feb 2009
    Location
    On The Mason-Dixon Line
    Posts
    577

    Default Re: Help

    Your bond is right in front of you - the grounding conductors .
    You are missing the proper Cable connector and the reidentifying of the white conductor to indicate it is a phase conductor as oppossed to a neutral conductor.
    I am basing this on your saying it's an AC subpanel, which I assume you are talking about a 240 volt disconnect for an Air Conditioning unit


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Help

    Quote Originally Posted by Scott Murdock View Post
    I don't see where this panel is bonded. I know you guys will set me straight. It is a AC subpanel.

    Scott,

    First things first ...

    That is on a house and not a submarine, therefore it is not a subpanel but simply a panel.

    Secondly, that is a 240 volt circuit which does not need a neutral, however, the white conductor is not permanently re-identified as is required when white conductors are used as hot conductors.

    The enclosure is grounded by the attachment of the ground.

    The NM cable is required to be in a clamp.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Scott Murdock's Avatar
    Scott Murdock Guest

    Default Re: Help

    Quote Originally Posted by Jerry Peck View Post
    Scott,

    First things first ...

    That is on a house and not a submarine, therefore it is not a subpanel but simply a panel.

    Secondly, that is a 240 volt circuit which does not need a neutral, however, the white conductor is not permanently re-identified as is required when white conductors are used as hot conductors.

    The enclosure is grounded by the attachment of the ground.

    The NM cable is required to be in a clamp.
    Thank you Jerry. That is what I was looking for.