    Sep 2008
    so so, California
    Default Question RE: UL 489
    The UL 489 Standard allows for two types of
    ratings. Standard circuit breakers cannot exceed
    a maximum of 50°C temperature rise at the wire
    terminal connection at 100%current in 40°C open
    air. 100% rated circuit breakers may have a
    temperature rise of 60°C at the wire terminal
    connection in the smallest allowable enclosure if
    the circuit breakers are connected with wire rated
    at 90°C wiring insulation sized to the 75°C chart
    Just wondering when they speak of "rise", are they referring to the CB being at a 40 degree C exterior ambient temp and then allowing a 50 degree C rise?
    Mar 2009
    Colorado Front Range
    Default Re: Question RE: UL 489
    That's what it says. And yes, at 226°F it's "hot" to the touch.
    Sep 2008
    so so, California
    Fantastic, thanks.
    I do my best not to touch the "wire terminal connection".