Results 1 to 13 of 13
  1. #1
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Service Conduit With Expansion Fitting

    This is obviously less than 6 feet in lenght. However, it is subject to extreme temperature changes. Do you recommend an expansion fitting. It appears there has been previous movement along the joint.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Nov 2009
    Location
    St Paul, MN
    Posts
    1,630

    Default Re: Service Conduit With Expansion Fitting

    I'd look closer at the foundation. From the cracked bricks in the photo it's possibly sheared and the movement caused the conduit to come apart.

    If there is no foundation issue I wouldn't recommend a specific repair, but "review and repair by a qualified electrician".

    MinnesotaHomeInspectors.com
    Minnesota Home Inspectors LLC
    ASHI #242887 mnradontesting.com

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Service Conduit With Expansion Fitting

    Quote Originally Posted by mathew stouffer View Post
    This is obviously less than 6 feet in lenght. However, it is subject to extreme temperature changes. Do you recommend an expansion fitting. It appears there has been previous movement along the joint.
    I agree with Ken. The slip fitting is actually more for movement of the ground that the underground SE is in and not for thermal expansion/contraction.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Service Conduit With Expansion Fitting

    Of much more concern here is whether the wire inside the conduit is being stretched and possibly pulled against hardware in the meter can that will cause a short. Pulling a couple of inches of slack can be a major issue sometimes.


  5. #5
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Service Conduit With Expansion Fitting

    There is no foundation movement. The masonry was loose and missing in areas from poor craftsmanship, but that's it.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Service Conduit With Expansion Fitting

    Expansion joints/slip fittings are not intended for use in that location, they are for thermal expansion/contraction.

    You would NOT want to use one there to allow for soil movement as you would want the conduit to stay put, for the reason Bill gave.

    Hang that conduit in place, let the soil move around the conduit, but don't let the conduit move because of the soil, you might just end up with exposed conductors after it mover 'too far'.

    The right one is not seated all the way in the top of that coupling, look at that angle.

    Missing seal on the power company access cover too.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Service Conduit With Expansion Fitting

    Quote Originally Posted by Jerry Peck View Post
    Expansion joints/slip fittings are not intended for use in that location, they are for thermal expansion/contraction.
    I had learned just the opposite. When I lived in MS where we had very expansive soils they required slip fittings midway between SE conduit and the panel or meter.

    Is if for the expansion/contraction of the conduit?

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Service Conduit With Expansion Fitting

    Quote Originally Posted by Scott Patterson View Post
    I had learned just the opposite. When I lived in MS where we had very expansive soils they required slip fittings midway between SE conduit and the panel or meter.

    Is if for the expansion/contraction of the conduit?
    Yes, those are for expansion and contraction of the conduit, no way would you want the conduit to rise and fall with the soil, you would want the soil to rise and fall around the conduit.

    Otherwise you could very well end up with a slip fitting and conduit being separated and leaving exposed conductors with no protection from physical damage.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Service Conduit With Expansion Fitting

    Quote Originally Posted by Jerry Peck View Post
    Yes, those are for expansion and contraction of the conduit, no way would you want the conduit to rise and fall with the soil, you would want the soil to rise and fall around the conduit.

    Otherwise you could very well end up with a slip fitting and conduit being separated and leaving exposed conductors with no protection from physical damage.
    Thanks!

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  10. #10
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Service Conduit With Expansion Fitting

    So would you want expansion and contraction of the conduit at that joint. The reason I brought it up, is becasue the fitting in the photo is cracked, likely from expansion of the fitting during freeze thraw.


  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Service Conduit With Expansion Fitting

    Quote Originally Posted by mathew stouffer View Post
    So would you want expansion and contraction of the conduit at that joint. The reason I brought it up, is becasue the fitting in the photo is cracked, likely from expansion of the fitting during freeze thraw.

    Mat,

    There should not be anything in that conduit which would crack it due to freeze/thaw.

    If the freeze/thaw is the soil moving, then the soil should be moving around the pipes.

    Hard to tell from the photo, but it looks like that simply was not installed all the way into the coupling, probably because the conduit from above and below are at an angle to each other.

    The conduits are there for protection from physical damage, they are presumed to not be water tight, so all conductors in them should be suitably rated for getting wet.

    Those should also be Schedule 80 PVC, not Schedule 40, which they probably are, as Schedule 40 is not rated to provide protection from physical damage - Schedule 80 is.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Service Conduit With Expansion Fitting

    Thanks


  13. #13
    John Steinke's Avatar
    John Steinke Guest

    Default Re: Service Conduit With Expansion Fitting

    In some areas it is common, even required under local rules, to have an expansion fitting where the service exits the ground.

    The purpose of this fitting is to allow the conduit to move with the ground, as the annual frost cycle causes the ground to heave.

    There is certainly no violation in having such a fitting anywhere- even if it's not needed.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •