Results 1 to 16 of 16
  1. #1
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Copper or aluminium Wire

    This was a condo built in 1981. Grounds and neutrals in the panel are copper, although the conductors appeared to be aluminium at the breaker terminal. This may be a dumb question but it would not be my first nor last, but is this simply discoloratoin or are these copper coated. The pics suck.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Copper or aluminium Wire

    I can't see anything worthwhile in the photos. However, 1981 was after AL wire was commonly installed. I have never seen a cable with both CU and AL mixed.

    Did you check the cable sheath for any identifying marks?


  3. #3
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: Copper or aluminium Wire

    That big open knock-out at the top needs to be filled.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  4. #4
    Join Date
    Nov 2009
    Location
    St Paul, MN
    Posts
    1,630

    Default Re: Copper or aluminium Wire

    To me the service wires appear to be stranded aluminum with an anti-oxidant compound on them. It's hard to tell though from the picture.

    MinnesotaHomeInspectors.com
    Minnesota Home Inspectors LLC
    ASHI #242887 mnradontesting.com

  5. #5
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,592

    Default Re: Copper or aluminium Wire

    Although I can't see much in the picture, it's got to be copper.

    Since they used NM-sheathed cable, the neutrals, grounds and hots all come from the same sheath. So if the first 2 are copper, so is the third.

    Dom.


  6. #6
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Copper or aluminium Wire

    The larger stranded wires on the right and the big feeders are Al. We can't see the connections of the solid branch wires at the breakers, but as was said above, they are copper by default if the neutrals are copper.
    Black and white pics at a lower resolution would be better.


  7. #7
    Join Date
    Jul 2007
    Location
    Chicago
    Posts
    928

    Default Re: Copper or aluminium Wire

    Matt are you referring to the feeders?

    Aluminum is common in that case .


  8. #8
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Copper or aluminium Wire

    No the branch wires at the breaker terminals. You can not see them in the photos, but when I shined my flashlight on them they looked like aluminium. Plus I scratched a few of the neutrals and I did not look like copper beneath the scratches. Maybe it was the crappy lighting.


  9. #9
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Copper or aluminium Wire

    The house is wired with Aluminum and Copper circuits.


  10. #10
    Join Date
    Jul 2007
    Location
    Chicago
    Posts
    928

    Default Re: Copper or aluminium Wire

    On enhancement I can see where the first and third neutrals from the right side look like they may be Aluminum.

    Try going to your original and reading the jackets.


  11. #11
    Join Date
    Nov 2009
    Location
    St Paul, MN
    Posts
    1,630

    Default Re: Copper or aluminium Wire

    Could be tin coated copper. If possible always look at the cut ends for confirmation.

    MinnesotaHomeInspectors.com
    Minnesota Home Inspectors LLC
    ASHI #242887 mnradontesting.com

  12. #12
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Copper or aluminium Wire

    Quote Originally Posted by Ken Rowe View Post
    Could be tin coated copper. If possible always look at the cut ends for confirmation.
    I haven't seen coated copper except in the very old rubber insulated cables, none of which were plastic sheated NM.


  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Copper or aluminum Wire

    Quote Originally Posted by mathew stouffer View Post
    but when I shined my flashlight on them they looked like aluminium. Plus I scratched a few of the neutrals and I did not look like copper beneath the scratches.

    Mat,

    Sounds like they might be copper clad aluminum, which is treated and rated like aluminum.

    You did notice all those NM cable in those clamps or bushings (whichever they are), and the top open KO (which was mentioned by others), and the the whites used for hot conductors, and the multiple taps, and what look like cut off strands of the feeder conductor stranded grounding conductor, and the stranded grounding conductor of the feeder being split into more than one terminal, and ...

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  14. #14
    Tim Spanos's Avatar
    Tim Spanos Guest

    Default Re: Copper or aluminium Wire

    more than likley it is copper clad aluminum cable where the inner core is aluminum and outer coating is copper...installer may have stripped ungrounded conductor on wrong gauge and removed copper coating and exposed aluminum..


  15. #15
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Copper or aluminium Wire

    Thanks guys. So copper clad aluminium have a smiliar failure rate as solid strand aluminium?


  16. #16
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Copper or aluminium Wire

    Quote Originally Posted by mathew stouffer View Post
    Thanks guys. So copper clad aluminium have a smiliar failure rate as solid strand aluminium?
    First of all, I know nothing about Copper clad Al as used in branch circuit wiring. However, in electronics, the "skin effect" refers to the fact that the outer skin conducts more current. So it stands to reason that copper clad Al is a better conductor and would be less likely to have expansion problems from heat build-up. There is less likelyhood of tarnishing as well, except where the Cu is scraped off. One bad is the Al core is still going to be brittle, so breakage is one thing that would be a concern.

    I got this much from inspectapedia:
    K. HOMES WITH COPPER-CLAD ALUMINUM WIRE
    Copper-clad aluminum wire has a thin copper outer skin and a core of aluminum.
    Therefore it looks like copper, except on close examination of a cut end.
    Markings on the cable jacket would include "Al" or "Aluminum". There is no known
    history of connection overheating problems associated with copper-clad aluminum
    wire. No corrective actions are required for copper-clad aluminum wire.
    L. MISIDENTIFICATION - PLATED COPPER WIRE
    Plated copper wire is relatively common in older homes, and it looks like
    aluminum wire. It was commonly used with rubber-based insulation. Identification
    can be made by careful inspection of a cut end of the wire. In general, plated
    copper wire would not be present in nonmetallic sheathed cable ("Romex"), it is
    most generally found in metallic sheathed cable ("BX"). Cable of the "BX" type
    is not likely to contain aluminum wire.

    http://www.inspectapedia.com/aluminum/alreduce.pdf




    Last edited by John Kogel; 11-24-2009 at 04:11 PM.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •