    Colorado Springs, CO
    Default 120/208v 3-Phase 400-Amp FPE Stab-Lok Panel
    120/208v 3-Phase 400-Amp Federal Pacific Electric Panel !!!
    I had no idea Stab-Lok panels were made this large. I ran across this one on a commercial inspection today.
    I checked building permits for the building and, lo and behold, what did I find? An electrical permit from 1990 to "REPLACE 400 AMP PANEL DUE TO A FIRE".
    The first photos are of the main disconnect outside the building. Those 400 amp fuses are HUGE!
    The tab for the panel latch is broken off and I was able to simply raise the panel cover to open it. That is a serious accident waiting to happen.
    Bruce Breedlove
    www.avaloninspection.com
    Default Re: 120/208v 3-Phase 400-Amp FPE Stab-Lok Panel
    Here is the 400-amp FPE Stab-Lok panel. This is the largest Stab-Lok panel that I have run across. I assume this is the panel that was replaced in 1990 after a fire. What a great opportunity missed.
    Notice the numerous openings around the breakers waiting for a finger to enter.
    I did not find any super loose breakers in the Stab-Lok panel but interestingly I did find a couple of overheated neutrals at a downstream panel.
    Bruce Breedlove
    Chico,Ca
    A big issue I see is the paralell conductors in lugs that may not be rated for more then 1 conductor in the fusible switch & the panel.
    Along with the grounding conductor in the neutral terminal bar at the downstream panel, and ... too many other things to mention.
    All were duly noted. I was amazed at how many open splices and open junction boxes I found above the acoustic ceiling tiles.
    Bruce Breedlove
