    Default Would a heat pump do this ? Have not seen before

    I inspected a 10 year old house with a heat pump. Outside temp was 38 degrees. Inside was 60 degrees. I went to the thermostat and set the temperature to 61 and the condensor did not come on, so I set it to 62 and the condensor came on. I went outside and noticed the condensor was loud and then noticed the fan was not moving. I turned the unit off. On my way inside I was wondering if the condensor fan could be themostatically controlled to not spin in cold are (outside air temp was 38). I dont think that is the case but I have been wrong before. Has anyone seen a condensor that the the fan would not come on in certain temperatures ?

    Gene

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Would a heat pump do this ? Have not seen before

    Gene, it is possible that the heat-pump was in defrost as soon as it came on. It is more likely the outdoor fan was seized. The quick and dirty way to tell is to feel the temp of the gas (large) refrigerant line at the out door unit. If it is in defrost, it will be cool (not cold). If it is in the heat mode, it will be warm (approaching Hot). Also if the fan is seized you can normally feel the top of the unit where the fan mounts and it will probably be hot if its seized.


  3. #3
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Would a heat pump do this ? Have not seen before

    VH nailed it, Sounds like defrost to me.
    The fan will be off during defrost but would not be thermostatically controlled during the heating cycle.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  4. #4
    Join Date
    Apr 2008
    Location
    McKinney Texas
    Posts
    501

    Default Re: Would a heat pump do this ? Have not seen before

    Jim and Vern, I forgot to emphasize that the compressor was noticabley very loud...made me think it might seize up. How does that sync with your thoughts on this unit?

    Thanks

    Gene


  5. #5
    David Bell's Avatar
    David Bell Guest

    Default Re: Would a heat pump do this ? Have not seen before

    Is it possible that the fan motor was making all that noise? There are units that operate the fan by pressure, but not likely on a ten year old residential.


  6. #6
    Join Date
    Apr 2008
    Location
    McKinney Texas
    Posts
    501

    Default Re: Would a heat pump do this ? Have not seen before

    Dave, I am sure the noise was from the compressor, not the fan.

    Thanks

    Gene


  7. #7
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Would a heat pump do this ? Have not seen before

    Quote Originally Posted by Gene South View Post
    Jim and Vern, I forgot to emphasize that the compressor was noticabley very loud...made me think it might seize up. How does that sync with your thoughts on this unit?

    Thanks

    Gene
    If it was in the first part of the defrost cycle the compressor does make extra noise for a short time while pressures equalize.

    One other thing that can make a lot of rattling and maybe sound like a bad compressor is a bad contactor relay. A bad relay would prevent the fan from running as well as the compressor.


  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Would a heat pump do this ? Have not seen before

    Quote Originally Posted by Gene South View Post
    Jim and Vern, I forgot to emphasize that the compressor was noticabley very loud...made me think it might seize up. How does that sync with your thoughts on this unit?

    Thanks

    Gene
    Normal if you caught it just entering defrost. Of course I was not there but it is normal for them to get noisy during defrost as pressures change. Mine wakes me up on occasion just due to the change in sounds from the outdoor unit.

    I inspected a 10 year old house with a heat pump. Outside temp was 38 degrees. Inside was 60 degrees. I went to the thermostat and set the temperature to 61 and the condensor did not come on, so I set it to 62 and the condensor came on. I went outside and noticed the condensor was loud and then noticed the fan was not moving. I turned the unit off. On my way inside I was wondering if the condensor fan could be themostatically controlled to not spin in cold are (outside air temp was 38). I dont think that is the case but I have been wrong before. Has anyone seen a condensor that the the fan would not come on in certain temperatures ?
    By the way, the outdoor unit is not the condenser... during heating (except during defrost) which is the reason I try to use "outdoor unit and indoor unit." The condenser is actually inside during heating operations

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Join Date
    Apr 2008
    Location
    McKinney Texas
    Posts
    501

    Default Re: Would a heat pump do this ? Have not seen before

    Hi Jim, yes. good point. Thanks

    Gene