    This just doesn't look right thoughts and a little help. The trap appears to ber located too low . There is a hard celing above so I am not sure what this is for, a bath has been added in the basement and this appears to be going to the hall bath on first floor. Laundry stack picture added as humor

    Member Benefits1

  2. #2
    Gary Boyet's Avatar
    Gary Boyet Guest

    Default Re: A little help

    Not sure pictures uploaded-first time utrying to upload pictures

    Attached Files Attached Files

  3. #3
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: A little help

    Looks like he did it . . .




  4. #4
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: A little help

    This may apply

    2006 IRC
    " P3201.6 Number of fixtures per trap. Each plumbing fixture
    shall be separately trapped by a water seal trap. The vertical
    distance from the fixture outlet to the trap weir shall not exceed
    24 inches (610 mm) and the horizontal distance shall not
    exceed 30 inches (762 mm) measured from the center line of
    the fixture outlet to the centerline of the inlet of the trap"


    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.