Results 1 to 4 of 4
  1. #1
    brianmiller's Avatar
    brianmiller Guest

    Default Panel installation

    Please tell me that installing the panel cover ontop of the metal siding used as a wall covering as gotta be wrong...if the panel become energized somehow, then that metal wall covering would become energized , correct...this has gotta be wrong, right?

    b

    Similar Threads:
    Last edited by brianmiller; 07-02-2013 at 04:40 PM.
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Panel installation

    If the enclosure projects as far through that metal as it should, there should not be a problem. After all, the enclosure IS (supposed to be anyway) GROUNDED, and the cover properly mounted to the enclosure is also grounded. And I would want that metal siding grounded too.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    brianmiller's Avatar
    brianmiller Guest

    Default Re: Panel installation

    thanks, jerry...I'll ponder your response for awhile....

    b


  4. #4
    Roger Frazee's Avatar
    Roger Frazee Guest

    Default Re: Panel installation

    Quote Originally Posted by brianmiller View Post
    thanks, jerry...I'll ponder your response for awhile....

    b
    Not all that uncommon to see a distribution panel / load center mounted to a metal surfaced wall. Like Jerry said as long as the metal on the wall is bonded to the effective ground fault path it should not be a problem.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •