Thread: rafter size
    Robert A. Kuzmick's Avatar
    Robert A. Kuzmick Guest
    Default rafter size
    In a cabin that is 20' front to back by 25'wide, I plan on using 2x8 on 12" ctr for rafters on a vaulted ceiling. Underneath will be an exposed beam. Snow load is pretty heavy as it is in upstate NY. Should I switch to 2x10 rafters on 12' ctr? Currently, there are trusses that have been damaged by previous owner(ie: cut/sistered/etc) Any input is very appreciated.
    Colorado Springs, CO
    Default Re: rafter size
    You should pay an engineer (or an architect with access to an engineer) to design this for you.
    Bruce Breedlove
    www.avaloninspection.com
    The charts I have require the following info. in order to figure.
    Horz. span (not rafter length) of rafter
    On center spacing used
    light or medium or heavy roof covering
    live load required by code in lb per SF
    dead load required by code in lb per SF
    drywall ceiling or not
    wood species used
    lumber grade used
    This is what I know Bruce:
    1. 20' span
    2. 12 oc
    3. medium-I'm putting on a metal roof over existing shingles.
    4. live load-minimal,
    5. dead load = 60
    6. no drywall. t&g pine
    7. spf
    8. #2
    thanks,
    Are you sure about the 60 psf dead load? Is that due to the T&G ceiling or code?
    The best match I can find in the tables are:
    50 psf live
    15 psf dead
    SPF is not even in the table, too weak probably even if 2x12.
    Southern Yellow pine on 12" centers:
    #2 2x10 = 17' 5" span
    #1 2x10 = 19' 5" span
    #2 2x12 = 20' 5" span
    Hem-Fir will not work unless #1 grade = 20' 5" span
    D.Fir-L
    #2 2x12 = 19' 8" span
    #1 2x12 = 20' 9" span
    Select Structural grade (special order) 2x10 = 20' 3"
    I would consider eng. I-joists for this application.
    i-level.com or search for engineered I-joists
    These products come with free eng advice.
    Quote Originally Posted by Robert A. Kuzmick View Post
    1. 20' span
    No, as you described it, it's a 10 foot span for the rafters, unless you are planning on a 'shed' style roof.
    Yep. 10' span. You should think about hiring an engineer or an architect with an engineer to design the roof for you. In my neck of the woods Regional Building Dept. would require the roof design to have a PE stamp before they would issue a building permit.
    Bruce Breedlove
    Philip Desmarais's Avatar
    Philip Desmarais Guest
    The higher the pitch the more impact on the roof by wind. I would think pitch would need to be considered.