    Default 10 amp outlet/receptacle circuits?

    Inspected a house yesterday which had numerous 10 amp circuit breakers protecting mulitple receptacle circuits. I've never seen 10 amp circuit breakers used before. I think I know and my Code Check Guide confirms that bedroom receptacle circuits should be min. of 15 amp and kitchen should be served by min of 2 20 amp circuits.

    Is there/what is a scenario where 10 amp circuits are used appropiately?

    This house was owner built by a contractor in 2004...Realtor of course informed me "you shouldn't find anything wrong with this house"

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Apr 2007
    Location
    state of jefferson
    Posts
    522

    Default Re: 10 amp outlet/receptacle circuits?

    check 240.6 nec! not a standard size but permitted. what does the panel listing indicate?


  3. #3
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Re: 10 amp outlet/receptacle circuits?

    Quote Originally Posted by brian schmitt View Post
    check 240.6 nec! not a standard size but permitted. what does the panel listing indicate?
    I don't have a copy of the complete NEC. My code check references 210.3 with the following...

    Branch circuit ratings for other than individual circuits must be 15A, 20A, 30A, 40A, or 50A

    I interpreted "individual" as serving a single outlet, as in one receptacle..which these were not. I hope that was an accurate interpretation, because I called it out as a defect requiring corection by a licensed electrician. Was I incorrect?

    As for reading the panel label...guilty as charged....relatively new at this and my process is still not ideal.


  4. #4
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    745

    Default Re: 10 amp outlet/receptacle circuits?

    240.6 Standard Ampere Ratings.
    (A) Fuses and Fixed-Trip Circuit Breakers. The standard ampere ratings for fuses and inverse time circuit breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50, 60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300, 350, 400, 450, 500, 600, 700, 800, 1000, 1200, 1600, 2000, 2500, 3000, 4000, 5000, and 6000 amperes. Additional standard ampere ratings for fuses shall be 1, 3, 6, 10, and 601. The use of fuses and inverse time circuit breakers with nonstandard ampere ratings shall be permitted.


  5. #5
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: 10 amp outlet/receptacle circuits?

    In over 30 years of work I have never seen a 10 amp breaker in other than a control panel. Do you have pics?

    Did you see what size the branch circuit wiring was? I would suspect that it was no smaller than #14.


  6. #6
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Re: 10 amp outlet/receptacle circuits?

    Quote Originally Posted by Jim Port View Post
    In over 30 years of work I have never seen a 10 amp breaker in other than a control panel. Do you have pics?

    Did you see what size the branch circuit wiring was? I would suspect that it was no smaller than #14.
    Yes, it was no smaller than #14

    Alot of circuits for a 1475 sq. ft. house. There were four different GFCI circuits serving the kitchen counter each with three receptacles...didn't make any sense to me.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  7. #7
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: 10 amp outlet/receptacle circuits?

    Seeing this is a Square D QO panel I pulled an extra breaker out of the truck. I believe the 10 that the OP is seeing is the 10kA interrupting rating, not the breaker ampacity.

    To Op, Square D has the circuit ampacity on the handle. The interrupting rating is near the yellow SQuare D logo.

    Breakers need to be rated for available fault current. Typical ratings for this are 10kAIC and 22kAIC.


  8. #8
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Re: 10 amp outlet/receptacle circuits?

    I'm pretty sure you're right....boy do I feel like an idiot....fortunately, I figured it out this afternoon prior to uploading the report.

    I only have a couple of dozen inspections under my belt and this house was the newest I've done by about 15 years. Looks like the interrupting rating on these newer breakers is printed much bigger than it was previously. When I inspected the panel everything looked okay to me, but all those kitchen circuits kept nagging at me, then I think my mind went into overdrive and my minds eye kept seeing all those big "10s" and my imagination took over from there.

    What's a rookie learn from this...

    1. Take really good close up pics of the panel.
    2. Never second guess yourself after you've left the house.
    3. Don't rush to deliver the report....if you've got a concern, don't guess, research it and go back to the house if necessary. Better to be late and get it right than on time and get it wrong.


  9. #9
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: 10 amp outlet/receptacle circuits?

    Quote Originally Posted by Robert Foster View Post
    boy do I feel like an idiot....
    However, that's approximately 10% of the idiot you would have felt like if you hadn't asked.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  10. #10
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: 10 amp outlet/receptacle circuits?

    How old is this installation? I have read on one of the electrical forums where some folks used 10 ampere circuit breakers to avoid using AFCI's, Arc Fault Circuit Interupters are just snake oil but they are a code requirement.