    Default exposed cable run

    Is extra protection required here?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Ron Bibler's Avatar
    Ron Bibler Guest

    Default Re: exposed cable run

    Nice hand rail... They should have ran it with the stairs

    Best

    Ron


  3. #3
    Join Date
    Apr 2007
    Location
    state of jefferson
    Posts
    522

    Default Re: exposed cable run

    Quote Originally Posted by Jon mackay View Post
    Is extra protection required here?
    no! just your usual protection


  4. #4
    JD Weekley's Avatar
    JD Weekley Guest

    Default Re: exposed cable run

    Well, I don't think that's Mike Holmes approved....


  5. #5
    Join Date
    Mar 2007
    Location
    Nampa, Idaho
    Posts
    601

    Default Re: exposed cable run

    The cable should be repalced with conduit or re-routed through wall cavity.


  6. #6
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: exposed cable run

    334.15 Exposed Work.
    In exposed work, except as provided
    in 300.11(A), the cable shall be installed as speci
    fied
    in 334.15(A) through (C).

    (A) To Follow Surface.
    The cable shall closely follow the
    surface of the building
    finish or of running boards.

    (B) Protection from Physical Damage.
    The cable shall be
    protected from physical damage where necessary by rigid
    metal conduit, intermediate metal conduit, electrical metallic

    tubing, Schedule 80 PVC rigid nonmetallic conduit, or
    other approved means. Where passing through a
    floor, the
    cable shall be enclosed in rigid metal conduit, intermediate
    metal conduit, electrical metallic tubing, Schedule 80 PVC
    rigid nonmetallic conduit, or other approved means extending

    at least 150 mm (6 in.) above the
    floor.

    Looks like (A) has been followed. Physical protection is a judgement call, but, IMO the cable could be possibly damaged by a vacuum.



  7. #7
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: exposed cable run

    Anywhere a dog can chew on it should have protection.

    But like Jim says, it's a judgement call and the code leaves it up to "where necessary".

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  8. #8
    Join Date
    Feb 2010
    Location
    Omaha
    Posts
    143

    Default Re: exposed cable run

    it there to hang socks for drying